DK- the basis of your arguement is the use of a fusing factor mate (1.45).
Firstly I'm not using fuses and second I'm not supplying machines with high starting currents, just general purpose socket outlets.

Can you now see why the IET get on my ----.

i keep out of these as much as i can as i cant express myself clearly with the written word, but

BOLL*CKS

how can you take all this information, that the IET has supplied, use graphs that the IET have supplied, and use calculations that the IET advise, and apply them wrongly, then blame the IET.?

if you dont like the IET, dont follow it, do your own research, make up your own understandable regs based on YOUR research results, because as you know BS7671 is not mandatory.
and if the worst happens and you go to court you can produce your own regs in evidence, if researched correctly, youll not have a problem.

when i first saw this thread i did a quick calculation on a basic 6a lighting circuit, using your method, and we would all be wiring in 4mm
 
Jonny - for a 32amp BS EN breaker to automatically disconnect a circuit after an hour that circuits' load would need to be 'greater than' the I2 value of 46amps (more like 47amps or 48amps).
I think somebody at the IET getting their calculations arse about face 'again'!

Ask yourself a question "how can a circuit breaker that wil not automatically disconnect a circuit at all at a load current of 46amps, automatically disconnect a circuit after an hour at a load current of 36amps"? There is no logic to your suggestion.
 
I understand where your initial argument/debate is generated from but reg 433.1 actually states the design of the circuit is unlikely to have a small overload for a long period... if you are in the senerio you are debating about then the circuit has been designed wrong and you are in breach of the regs anyway... the senerio you are using as you defense should not occur for a long duration, short duration can be acceptable and is common on some old ring mains and even if you had a cable for example rated at 36 amp pulling say 45amps its been allowed for by the research into the structure and tolerances of the cables we use.

Ive seen over my many yrs cables drawing 15+ amps past their rating for yrs before ive come across them and other than been discoloured slightly they are still holding integrity (well just) but these conditions were caused because copper wire had been fitted in place of fuse wire thus overload wasn't detected...yes they ran quite warm but didn't fall apart or combust.

DK - you've resorted to talking rubbish here!
Once your installation is completed you've got to walk away and leave it for 5 or even 10 years before yu get a chance to come back and test it, in that time given enough faulty appliances you could have wasted enough energy run another installation for that entire period and thats' if the installation hasn't caught fire.
 
David, why do you think we carry our cable calculations? It is because we can then work out the correct cable size for the load. Do you not think that the IET when writing the regs take these things into consideration?

Or do you think one person writes the CCC of cable, someone else writes about where RCDs should be used, someone else measures and draws the curves for MCB tripping times and then don't communicate with each other?
 
DK - you've resorted to talking rubbish here!
Once your installation is completed you've got to walk away and leave it for 5 or even 10 years before yu get a chance to come back and test it, in that time given enough faulty appliances you could have wasted enough energy run another installation for that entire period and thats' if the installation hasn't caught fire.


I don't know how the fire brigade cope with so many electrical fires and the threats of cut backs in there jobs.
 
Just think, of all those ring circuits installed over the last 70+ years, (not to mention the Radials). ......All it seems were incorrectly protected, from the 30A 3036, 30A 1361, 30A Type 1+2 MCB's, and now the 32A Type B MCB's!! ...What a Revelation!! lol!!

How stupid are you son?
The problem has occured because BS EN breakers are different from BS breakers.
 
So what are you going to do now and in the future then, only wire 16A radials socket circuits??

The law of averages, tend to favour herds being on the right side of the line, while the maverick's are on the other!! lol!!

It's already obvious that you are a half wit son, but just for you:
4.0mm ring mains can be protected by 32amp BS EN breakers
2.5mm ring mains by 25amp
4.0mm (so called) radials 20amp
2.5mm (so called) radials 16amp
Not too complicated for you I hope.
 
It's already obvious that you are a half wit son, but just for you:
4.0mm ring mains ( ring final circuit)can be protected by 32amp BS EN breakers
2.5mm ring mains (ring final cirucuit) by (32 amp) 25amp
4.0mm (so called) radials (32amp)20amp
2.5mm (so called) radials (20 amp) 16amp
Not too complicated for you I hope.

For someone who likes to correct people when they are wrong you don't get an awful lot correct yourself do you.
 
dilb - the I2 values of BS EN breakers (or the curent rating below which they will not automaticaly disconnect) are much higher than the I2 values of BS breakers of the same nominal current value.

This in effect makes your job easier because if you simply drop a circuit breaker size (nominal rating) for each type of circuit (as described earlier), correction factors 'almost' cease to be an issue because there is a much larger gap between each of the I2 values of the circuit breakers and the maximum current carrying capacities of the cables used.
 