wildgoose

When I find existing gas/water/oil safety bonding, which has been satisfactorily connected of 6mm csa, I normally enter a comment on the certificate along the lines of "For Information Only: The safety earth bonding to the water and gas services is satisfactory but does not comply with latest BS7671 (2008) requirement".

If it meets the adiabatic requirements then surely there's little justification to upgrade it unless major refurb is being done. Was told by another spark today this is wrong as I should always be upgrading to 10mm safety earth bonds and 16mm main earths when ever a CCU change is done?
I always upgrade the main earth to 16mm but not the safety bonding - thoughts and comments appreciated please!
 
Last edited by a moderator:
The adiabatic equation must NOT be applied to main protective bonding conductors BS7671:2008+A1:2011 543.1.1

Main protective bonding conductors of installations where PME conditions apply, must be selected in relation to the largest supply Neutral conductor in accordance with BS7671:2008+A1:2011 Table 54.8 (eg. =<35mm[SUP]2[/SUP] copper Neutral conductor requires main bonding conductors of 10mm[SUP]2[/SUP] ).

Main protective bonding conductors of all other installations if copper must be >6mm[SUP]2[/SUP] but need not exceed 25mm[SUP]2[/SUP] BS7671:2008+A1:2011 544.1.

So providing PME conditions do not apply, existing 6mm[SUP]2[/SUP] main bonding conductors meet the current regulations and need not be upgraded.

In all cases, providing the existing main earthing conductor exceeds the minimum adiabatic size it also meets the current regulations and need not be upgraded BS7671:2008+A1:2011 543.1
 
Last edited by a moderator:
With PME and 6.0mm main bonding it is permitted to leave it if there are no signs of heat damage.....always upgrade if possible,but it's your call if you consider 6.0mm adequate.
 
With PME and 6.0mm main bonding it is permitted to leave it if there are no signs of heat damage.....always upgrade if possible,but it's your call if you consider 6.0mm adequate.
If services are convenient and close by then I will do the upgrade, but when the water stoptap is at the other end of the house and difficult to route then it's a different matter - especially if it still meets the electrical requirement!
 
Nonsense!! As already pointed out 6mm2 bonding is ok if the adiabatic is carried out and earthing conductor size is verified on a TN-S system. On P.M.E upgrading is advised but if you confirm that the existing 6mm2 is integral, no signs of overheating or corrosion is evident then a note on your cert will surfice.
 
agree. if it ain't broke, why fix it?
 
The only time this may be an issue is on a Multiple occupancy property on a P.M.E system located in the basement with feeds run in 16mm T&E with 6mm2 earth to individual flats. Main bonding terminated in flat instead of back at intake position and using the 6mm2 as a shared earthing and bonding conductor back to the intake. Normally here i would confirm the 6mm2 using the adiabatic as this is in theory a submain and then verify for no overheating or corrosion at termination points to flat fuseboard and s/f in basement. I would then note on the cert issued that 6mm size bonding exists between board and intake s/f position.
Any less than 6mm and it is then curse ya luck time to find a way back to the basement with a bigger sized earth cable or prey that the water and gas points are located next to the intake position before entering the flats!
 