When I find existing gas/water/oil safety bonding, which has been satisfactorily connected of 6mm csa, I normally enter a comment on the certificate along the lines of "For Information Only: The safety earth bonding to the water and gas services is satisfactory but does not comply with latest BS7671 (2008) requirement".
If it meets the adiabatic requirements then surely there's little justification to upgrade it unless major refurb is being done. Was told by another spark today this is wrong as I should always be upgrading to 10mm safety earth bonds and 16mm main earths when ever a CCU change is done?
I always upgrade the main earth to 16mm but not the safety bonding - thoughts and comments appreciated please!
If it meets the adiabatic requirements then surely there's little justification to upgrade it unless major refurb is being done. Was told by another spark today this is wrong as I should always be upgrading to 10mm safety earth bonds and 16mm main earths when ever a CCU change is done?
I always upgrade the main earth to 16mm but not the safety bonding - thoughts and comments appreciated please!