I've recently wired a boiler frost and pipe stat from the permanent live of the 10-way control centre which is supplied via an SFCU fitted with a 3amp fuse. However, the heating engineer on site has told me that it should be from a supply which has nothing to do with central heating, so that it cannot be accidentally switched off when the boiler is isolated. I did explain that this would result in 2 supplies at the control centre, and provided that the sfcu is labelled to warn against accidental isolation, it is better to have the whole central heating system isolated by one source. Your views would be appreciated.
 
I'd say you were right about them - it will be wired as part of the controls - if the "heating engineer " has his way you'll wire the frost protection side seperate and he'll switch off the heating side result frozen boiler !
 
I too would say your right. Heating Engineers are only plumbers who can't stomach the s**tty side of the job.
 
If the boiler is turned off/isolated then the frost stat becomes totaly redundant anyway....as there's no boiler it can turn on (as it's supply is switched off).

I'd personaly use the same supply for heating and frost stat as it's all part of the same system......1-0 to Guitarist on this one.
 
Tell him to accept that he is a failed electrician and leave the proper electrician to do the job ha ha
 
I worked for a Swiss controls company tell him he is talking tosh because when you switch the control panel off then everything should be isolated Years ago I would argue with the heating guy that the frost stat on a AHU was to be fitted AFTER the frost coil not before. Their logic would be that when the air hits 0oC the unit will shut down but its function is to protect the AHU if the boilers trip ie if the air after the frost coil hits 5oC then it shuts the fan down.

The frost coil should control to 7oC hence why the frost stat is set for 5oC why because water expands at 4oC and not 0oC because by then the damage is done
 
Thanks for all the replies guys. I didn't want to go down the route of multiple isolation signs, and couldn't really see the benefit, just so long as the owner knows not to turn the sfcu off.

- - - Updated - - -

Tell him to accept that he is a failed electrician and leave the proper electrician to do the job ha ha

He earns a damn sight more than I do :)
 
So with his theory the boiler is isolated but don't worry the temp drops below min temp but thank god you didn't isolate the frost stat by accident phew, now it can do its job and fire boiler up, er no because the boiler is isolated, back to the drawing board for the plumber me thinks.
 