Cheers for the reply Jay,

Yeah the house is a 3 bed that was converted into 5 (front room and dining room) to cram in the students and make more money and the rooms are tiny but as there was only 1 bathroom in the house the showers were put into the rooms to make the house more useable.

I am registered with Elecsa and didn't know that classed me as scam member. Makes me laugh though as the "boys club" NICEIC is merging with Elecsa in April and will all be one company anyway so I've heard.
 
so take advice from elecsa. what else are you paying them £400+ /year for?

edit: bear in mind that you are responsible only for the work you do . as long as you make it clear on the cert. you ain't got much choice.
 
Last edited:
Cheers for the reply Jay,

Yeah the house is a 3 bed that was converted into 5 (front room and dining room) to cram in the students and make more money and the rooms are tiny but as there was only 1 bathroom in the house the showers were put into the rooms to make the house more useable.

I am registered with Elecsa and didn't know that classed me as scam member. Makes me laugh though as the "boys club" NICEIC is merging with Elecsa in April and will all be one company anyway so I've heard.

Its not an insult to you it's referring to the part p clubs themselves
 
Hmm, I think I'd be questioning the demand in that place. Five electric showers plus all the usual is a large load. Given that it's student accommodation there's a fair chance they'll all be in use at the same time when they're off out on the waz.

You're also going to have fun trying to split the loads across two RCDs to minimise nuisance tripping.
 
why do you have to do an EICR? youhave been asked to change the board and that is all you are responsible for surely, obviously you have to out in main bonding if not in place, Do IR testing on all circuits before you change the board to make sure you wont get any nusaince tripping, change the board test all circuits and then put the sockets in the bedrooms down as a deviation from the regs, and then point out to customer that this is not in line with the regs and recommend that they be moved or blanked off.
 
why do you have to do an EICR? youhave been asked to change the board and that is all you are responsible for surely, obviously you have to out in main bonding if not in place, Do IR testing on all circuits before you change the board to make sure you wont get any nusaince tripping, change the board test all circuits and then put the sockets in the bedrooms down as a deviation from the regs, and then point out to customer that this is not in line with the regs and recommend that they be moved or blanked off.


i concur. storm in a teacup. or a pi$$ into the wind. gvet it done, get paid, move on.
 
Jase,

was going to do an EICR first to see if the circuits were all sound and for the fact that there is no previous data for it. I know there is going to be things that will be picked up - the fact that there is no MPBC's for example. Don't see the point in changing the board then having to deal with any headaches that come up. You know what people are like, if I change the board and a circuit fails an IR test for example then they will see it as my fault as I touched it last then expect me to rectify it for free.

Just covering myself. Whenever I do a board change I always do the testing first
 
Hmm, I think I'd be questioning the demand in that place. Five electric showers plus all the usual is a large load. Given that it's student accommodation there's a fair chance they'll all be in use at the same time when they're off out on the waz.

You're also going to have fun trying to split the loads across two RCDs to minimise nuisance tripping.

exactly, hence my original comment, too many questions for a novice to seriously know the answers too haha
 