Why am I a scam member? The showers were fitted 3 years ago and the house built in 1960 so the sockets were already in place
i meant if you were niceic, elecsa or napit.
Why am I a scam member? The showers were fitted 3 years ago and the house built in 1960 so the sockets were already in place
Cheers for the reply Jay,
Yeah the house is a 3 bed that was converted into 5 (front room and dining room) to cram in the students and make more money and the rooms are tiny but as there was only 1 bathroom in the house the showers were put into the rooms to make the house more useable.
I am registered with Elecsa and didn't know that classed me as scam member. Makes me laugh though as the "boys club" NICEIC is merging with Elecsa in April and will all be one company anyway so I've heard.
Fair point telectrix - £505 a year!!!!
why do you have to do an EICR? youhave been asked to change the board and that is all you are responsible for surely, obviously you have to out in main bonding if not in place, Do IR testing on all circuits before you change the board to make sure you wont get any nusaince tripping, change the board test all circuits and then put the sockets in the bedrooms down as a deviation from the regs, and then point out to customer that this is not in line with the regs and recommend that they be moved or blanked off.
I will need to carry out a periodic first as there is no previous certification for any of the work (this was originally done 4 years ago).
Hmm, I think I'd be questioning the demand in that place. Five electric showers plus all the usual is a large load. Given that it's student accommodation there's a fair chance they'll all be in use at the same time when they're off out on the waz.
You're also going to have fun trying to split the loads across two RCDs to minimise nuisance tripping.