partypest
You're welcome mate. There are plenty of Electrical Trainee out there who have actually been doing it for years and have decided to be legit and do it properly. I know of some kitchen and bathroom people who quote this Reg and that Reg at me when they haven't got a clue about Ze or U or I or W. Good for you for going legit and I hope it pays off. Back to that garage supply though, you have now learned that some jobs need a bit more note taking and fact finding. This forum should be an excellent sounding board for ideas, but there are one or two grumpy old men and I hope they haven't put you off. My two pennies, before any further facts from you, would be to separate the supply to the garage on to it's own CU and RCD at the CU in the garage. If you're 'full scope' on NICEIC, you can sign this one off, if you're 'limited scope', you can't, as you're changing the protective device. I would also be very sure that you establish all the facts about the supply cable to the garage. Measure its resistance, compare that to what it should be for a cable of that estimated length etc. there could be joins/different cable etc. I'm glad to hear you want to do it right, and the only way to do that, is to be 100% sure with what you're connecting to, particularly with older installs. Good luck.