ir testing today on 6 circuits all >999 apart from sockets which was around >500 odd,

every socket unscrewed and walls being plastered no bags over sockets , im thinking this may be effecting the results , loose connection/condinsation etc
 
> 2Meg. is OK. >500Meg. be happy or you need to get alife.
 
lol

i know its a pass, 0.5M is the minimum

i wasnt saying it is a fail was wondering why the meter would >999 the rest and not the ring so obv something causing it .
 
ir testing today on 6 circuits all >999 apart from sockets which was around >500 odd,

every socket unscrewed and walls being plastered no bags over sockets , im thinking this may be effecting the results , loose connection/condinsation etc
Hard to please some folk
 
breathe on the crocs will lower the reading at that level.
 
Hard to please some folk

???????????????????????????????????????????????????????????????????????????????????????????????

mearly questioning why guys i havent failed it by lack of knowledge or even planning on any remedials
 
Put it into perspective,
@ 500Meg, you're leaking <1 µA, through resistance.
The circuit will be leaking considerably more than that through the capacitance of the cables when energised.
 
At those levels it could be anything but again nothing to worry about. Other option is to use a megger that only reads up to 299 Meg then you wouldn't even be asking this question. :lol:
 
Last edited by a moderator:
At those levels it could be anything but again nothing to worry about. Other option is to use a megger that only reads up to 299 Meg then you wouldn't even be admin this question. :lol:

lol good shout ill kewtech it >200 lol
 