Was travelling today in the snowdon ranges of Wales and noticed several similar looking transformers on the tops of poles.
It looked to be a single phase arrangement with 2 ht lines going in on heavily insulated posts. The output/s (4 terminals), looked like they we're 2 coils but only with one coil used. Presume the two central posts could have been strapped together and then the outer terminals used at a higher voltage if needed??
Got me thinking about what the likely input was. I'm guessing this was a phase and neutral arrangement at XXkv fed from a delta/star transformer.
Anybody enlighten me?
Pole mounted TX's are normally 11Kv delta - 400V star, the two lines are the Hv Ring main
But there were only two ht lines incoming instead of the normal 3 line delta configuration?
A web-link to a line diagram would be useful if anybody knows of one?
They are multicore, ring main in and ring main out
Never seen a pole mounted Ring Main Unit (RMU) Pretty pointless too!! An RMU is basically a dual fed switch unit feeding a take-off load switch, Switch Fuse, etc all at MV. It enables the load switch to be fed from either side of the RMU, through the RMU, or sections of the MV ring to be isolated without affecting any of the load switches. Or indeed to isolate a load switch etc!!
Without a photo it would be hard to determine what the OP has been looking at, as there are so many types of pole mounted TX's. Some will, only use two primary conductors, all depends on the internal set-up and what the LV side is being used for!!
and, sorry, E54 but your post is like the supply cables, way over my head. LOL.
I've seen some similar pic's on the internet and I think what I'm describing is a single phase (current) transformer, with HV input and LV output.
Since there were only 2 HV lines in and 2 LV lines out, this surely means that the likely 11KV input was a single phase and neutral line?
I'm just interested to understand what I was looking at and because I'm only experienced in ELV control and LV systems and not HV distribution??
There is no neutral on MV/HV transmission lines, only the 3 phases. The neutral is only seen on the LV side of the transformer, and is only a neutral when it's grounded!! You can still have 2 MV lines into a transformer and 240V out on the LV side, as i stated, far too many different configurations of distribution TX's, that can cover just about any provision required!!
Show us the pictures you've seen on the internet then.
The transformers were similar to this but with a casing designed to strap to poles.