Hi all, upgrading a customers shower to 9.8kw, original supply cable is 6mm.
At first I thought straight away of upgrading to 10mm but doing design calcs I think its ok to use the 6mm.
Design current 40A (not that they will ever have it full blast) 40a mcb backed up by 30ma rcd. And the cable is run loose above insulation then clipped direct. Just trying to save customer a bit of cash.
Any thoughts would be grateful, cheers
 
I know you said it runs above insulation but does it run through insulation at any point ?
9.8kw is more than 40A at 230V.
It will always be at "full blast" as showers achieve varying water temp by mixing heated water and cold, not by varying drawn current.
 
In some ways, you could argue that it's clipped direct on all of the run if it's only LAYING on the insulation.. and thus the CCC is 47A according to table F4(i) of the OSG, but if it gets buried, then you're down to 34A (officially).

But then you've got Volt Drop to account for too. What's the length of the run?

It's close.

If it was me, I'd sleep better having upgraded to 10mm.

I'll be interested in other peoples' views.

- - - Updated - - -

It will always be at "full blast" as showers achieve varying water temp by mixing heated water and cold, not by varying drawn current.

I kinda thought that, too.
 
In reality though a cable just laid on insulation will still suffer from the effects of reduced heat dissipation. Try sitting on a sheet of kingspan for ten minutes and see how warm your arse gets. If it was laid on insulation I would still derate to method 100 or maybe 102.
 
I know you said it runs above insulation but does it run through insulation at any point ?
9.8kw is more than 40A at 230V.
It will always be at "full blast" as showers achieve varying water temp by mixing heated water and cold, not by varying drawn current.
Showers have different power ratings at different voltages on the box, so might be a 10.5kw shower running at 230v hence him saying 9.8kw being the one he's calculating from, all in all 10mm all the way for me regardless of power if possible, alternatively lower rated shower and keep 6mm
 
Actually he must have used 240v for his calcs to come up with 40 amp
 
Last edited by a moderator:
The run is app 20M situated on ground floor extension, I can see run back to main building clearly in loft above all in insulation when it goes back into main building it runs in between ceiling of gr floor and floor of first floor.
 
how does a electric shower mix heated water and cold water?
normally there is only a cold feed to it
 
Lads excuse my ignorance to how the water is heated, I thought the shower was like an element and used more power the hotter u wanted the water?
 
The element will always draw FLC. It varies the temperature of the output water by cycling on and off, thereby mixing differing quantities of cold and heated water together to reach the desired temperature.
 
it's the flow rate that determines the temperature. if you incresa the flow, the water will be cooler as the heater does not have as much time to heat it. what i would do, in this case, would be to make sure the cable is not in contact with insulation, above or below it, then, with a 40A MCB, clamp it to see what it draws. as long as it's below 47A, 6mm is OK.
 
10mm for showers everytime for me. What if they re insulate the attic space. A loose cable just lying over the insulation? Not a great method of installation imo.
 
Thomas you are right there mate, going to re run a 10mm cable, better to be safe than sorry and all that. Would rather they get an 8kw shower but the thing they have brought is all singing all dancing. Thanks for the input guys :)
 