Sparky28
Hi all, upgrading a customers shower to 9.8kw, original supply cable is 6mm.
At first I thought straight away of upgrading to 10mm but doing design calcs I think its ok to use the 6mm.
Design current 40A (not that they will ever have it full blast) 40a mcb backed up by 30ma rcd. And the cable is run loose above insulation then clipped direct. Just trying to save customer a bit of cash.
Any thoughts would be grateful, cheers
At first I thought straight away of upgrading to 10mm but doing design calcs I think its ok to use the 6mm.
Design current 40A (not that they will ever have it full blast) 40a mcb backed up by 30ma rcd. And the cable is run loose above insulation then clipped direct. Just trying to save customer a bit of cash.
Any thoughts would be grateful, cheers