Hi all, was ask to go and look at a temporary supply for a new build on an old farm.

The mains has been moved to a small hut with a 4way garage cu
63A 30mA rcd 2x 16A mcb's, Cut-out has 60A fuse fitted

Has a 3/8 1.2mtr earth rod just under supply pole
240V mains present but as soon as you draw to much off the single socket it trips
will charge a mobile and run a lead lamp but drills, grinders all gwo, trips out

I have read the treads that say it should have a 100mA S type rcd and more rods or,
could it be a supply problem.
will be carrying out further tests soon for now only voltage. Any help before my return would be great. Thanks
 
As Murdoch says above, you need to get your tester out and start testing first. Ze, loop tests, IR , RCD tests, etc etc
 
What trips?? lol!!

If it's the RCD, then you either have a circuit connection fault or RCD is a duffy!! ...lol!!
As others have stated ... get your test kit out and use it, .....If your an electrician that is!! If not then get a qualified electrician in to sort the problem out for you!!
 
After reading some of the threads, I thought the same only never had any problems with TT in Towns, never worked on any farms

Yes I do its the yellow one everybody loves?

??

What tests have you done then.
 
Yeah I think a Ze test is needed, loop and IR/RCD the cu is new and its got a single radial with 2.5 less than 200mm and cable is visually new and undamaged all connections tight
 
Yeah I think a Ze test is needed, loop and IR/RCD the cu is new and its got a single radial with 2.5 less than 200mm and cable is visually new and undamaged all connections tight


I'd be asking if its new, who installed it? and where is the cert so you can compare the results!
 
the story goes... people bought farm, to build new house, knocked building/barns down, moved supply ran out of cash sold it on. I was told they spent over 100K???
Got a call to go take a look. The cu is on page 363 of the latest toolstation cat. and looks as good/new. The 6A mcb is on floor of hut and another 16A fitted N/C
 
Well, without wishing to point out the obvious, we could sit here all day and speculate..... or you go to site and do all the tests and post your results!
 
still not told us if it's the RCD or the MCB thast's tripping.
 