Thanks for reply's, just got my mtf back so testing tomorrow, may sink a longer rod or two. Will post my findings.
 
1: it was easy to pull the 3/8 rod out what seemed to be soft earth/mud and just as easy to sink (not in same hole).
2: had problems with Za in past where a longer thicker one solved problem, pig to get i.
Larger csa in contact with earth equals lower resistance, others are suggesting an earth plate maybe needed
 
I am struggling here! If your RCD is tripping, there will be an imbalance between your line and neutral currents somewhere in circuit. Check Ze before doing any earthing work you may not need to do! I suspect your problem lies within the circuits installed or an iffy RCD rather than any earthing issue.
 
I don't thinks so as you could draw and circuit diagram on a piece of A4 paper, so cut out-to meter to cu RCD 16A feeding dbl m/c skt and you could do it to scale
need to do Ze & RCD tests, thanks for helping think its got to be an earth problem.
 
I don't thinks so as you could draw and circuit diagram on a piece of A4 paper, so cut out-to meter to cu RCD 16A feeding dbl m/c skt and you could do it to scale
need to do Ze & RCD tests, thanks for helping think its got to be an earth problem.

Sorry mate you have totally lost me!
 
Yes I agree Ze & RCD testing first thing if good maybe supply transformer one pole away. I did have a brief look at it and imo, it's seen better days.
I might just earth it to a pylon or put in a 100A main switch in place of RCD and see if mcb trips.
 
A bigger rod.... MMMM

Whats changing the main earth going to do in this case?

What do you think is causing the RCD to trip and what tests would you perform in order to determine this ?
 