Doing an EICR on a property.
There are 5 properties in a block, the middle one is a sort of village hall and there are 2 retirement type homes either side. All have their own supply and the whole building is owned by some sort of Trust.
The EICR I'm doing is in the village hall.
Heating is from a oil fired boiler, the boiler is placed in an outbuilding of one of the adjacent properties. The supply to the boiler comes from the village hall. Oil pipe is not bonded, obviously an issue and I'm now trying to get my head around what needs doing, because also in the outhouse are some sockets from the property assocaited with it, with a fridge pugged into one socket.
So in effect there are 2 different supplies entering the outhouse, so when I bond the oil pipe do I bond it to the village hall supply, to the neighbours supply or both?
There are 5 properties in a block, the middle one is a sort of village hall and there are 2 retirement type homes either side. All have their own supply and the whole building is owned by some sort of Trust.
The EICR I'm doing is in the village hall.
Heating is from a oil fired boiler, the boiler is placed in an outbuilding of one of the adjacent properties. The supply to the boiler comes from the village hall. Oil pipe is not bonded, obviously an issue and I'm now trying to get my head around what needs doing, because also in the outhouse are some sockets from the property assocaited with it, with a fridge pugged into one socket.