yellowvanman

Doing an EICR on a property.

There are 5 properties in a block, the middle one is a sort of village hall and there are 2 retirement type homes either side. All have their own supply and the whole building is owned by some sort of Trust.

The EICR I'm doing is in the village hall.

Heating is from a oil fired boiler, the boiler is placed in an outbuilding of one of the adjacent properties. The supply to the boiler comes from the village hall. Oil pipe is not bonded, obviously an issue and I'm now trying to get my head around what needs doing, because also in the outhouse are some sockets from the property assocaited with it, with a fridge pugged into one socket.

So in effect there are 2 different supplies entering the outhouse, so when I bond the oil pipe do I bond it to the village hall supply, to the neighbours supply or both?
 
I'd bond it to the MET it's supplied from at the point it enters the village hall....but if you are doing an EICR why are you doing it?....just code it.
 
you bond it to the village hall MET , which is the building that the oil pipe introduces an earth potential into , sockets from another supply neither here nor there.
but as WP says just code it for the report.
 
Is the main supply to the boiler via a small CU from the village hall's CU?? If so, bonding of the oil pipe should be connected to that CU, especially if the supply is TNC-S. The heating pipes from the boiler, to be bonded as they enter each of the 5 properties back to those properties EMT which in turn will be connected to the MET, if the main supply for the 5 properties are derived from a single DNO service head (via a Ryefield panel or similar)....
 
Is the main supply to the boiler via a small CU from the village hall's CU?? If so, bonding of the oil pipe should be connected to that CU, especially if the supply is TNC-S.

Supply to boiler is off a fused spur on ring main through a coin meter. Supply to hall is TNCS, not sure what the supplies into the dwellings are but my experience of the rest of the village would suggest they are TNS.

The heating pipes from the boiler, to be bonded as they enter each of the 5 properties back to those properties EMT which in turn will be connected to the MET, if the main supply for the 5 properties are derived from a single DNO service head (via a Ryefield panel or similar)....

Boiler only heats the village hall, other dwellings have storage heaters. All 5 properties have their own DNO head. Where the boiler is in the outhouse there is also a small radiator off the boiler (not sure why as the outhouse is not insulated etc.), from there 2 pipes enter the village hall and I guess the 3rd pipe is the cold supply coming from hall to boiler. Boiler does not heat hot water, heating only.
 
That explains things a little better...lol!!

OK, If the supply into the village hall is TNC-S (PME), and the other properties are all in a block, then in all probability, the other properties will be too. As such, the supply into the outbuilding does not comply as it stands at the moment. So as others have suggested a 10 mm bonding conductor from the hall's MET will be required to comply with PME regulations.

The oil pipe as such is only from the storage tank to the boiler, depending whether it's been buried or not, may not require bonding, but the radiator heating pipes (water) from and too the boiler almost definitely will, as well as the water supply pipe, if metallic and have been buried. Always check this with a IR test and if < 23K ohms, ...Bond!!

Normally these oil fired boilers, are supplied via a modified CU, that incorporates din rail mounted control relays and timers etc. It keeps everything together in one box, ...so to speak!! lol!!
 
You may also find the oil pipe is staked down possibly by the tank

Not the pipe, but the tank!! And only if it's a metallic storage tank, many are now for want of a better description Plastic in nature!! If metallic, it was once a requirement to be earthed, for filling purposes between tanker and tank!! (static discharges and the like).
 
Just about all the oil pipes are staked down , where I live , Plastic or Steel tanks ........
 
What between the tank and the boiler?? Can't for the life of me understand that one?? Must have all been done by the same person then, who didn't know what the hell he was doing!! lol!!
 
That explains things a little better...lol!!

OK, If the supply into the village hall is TNC-S (PME), and the other properties are all in a block, then in all probability, the other properties will be too. As such, the supply into the outbuilding does not comply as it stands at the moment. So as others have suggested a 10 mm bonding conductor from the hall's MET will be required to comply with PME regulations.

The oil pipe as such is only from the storage tank to the boiler, depending whether it's been buried or not, may not require bonding, but the radiator heating pipes (water) from and too the boiler almost definitely will, as well as the water supply pipe, if metallic and have been buried. Always check this with a IR test and if < 23K ohms, ...Bond!!

Normally these oil fired boilers, are supplied via a modified CU, that incorporates din rail mounted control relays and timers etc. It keeps everything together in one box, ...so to speak!! lol!!

Spoke to Elecsa technical support before I saw your reply.

They have suggested:
Bond oil pipe to the MET of the property it enters (neighbours) and bond the water pipes that feed/return from the boiler at their point of enter into the village hall.

Which is basically what you have said and not very far away from what I expected. Thanks for the input!
 