Looked briefly at a job this afternoon for a builder i know,as i was bouncing between jobs,
Its 2 bed flat in a high rise block. Quite old, just from quick look and see what springs out method... lol find out a lot in 15 mins hahaha, if not less.
TN-S, 6mm 2 core armour cable to flat, 5 mtrs, dno supply DP isolator, there side all 25mm.
Flat has 6 way wylex with BS3036 fuses.
Took a few sockets off (metal clad) no cpc or flylead.
Ceiling roses again no cpc
Cooker no cpc.
Then seen it was wired in conduit, wondered if it was continuous. Done a quick R2 and had continuity back (yay)
Obviously we are looking at about 14th edition time of install im guessing. conduit used as cpc is fine, and i believe is still fine.
Not tried to use pipe and get new cpc to points dont know whats hidden in the concrete
my questions,
1. On my r2 test is impossible due to no cpc, so im i correct in putting N/A here and then record the R2 in its column.
2. Should i split the ring into radials, as cpc is a radial or leave as ring.
3. Anything i should mention on departures, ie the 20mm pipe as cpc.
Just looking for pointers to make sure i cover the bases with my cert.
Cheers
Its 2 bed flat in a high rise block. Quite old, just from quick look and see what springs out method... lol find out a lot in 15 mins hahaha, if not less.
TN-S, 6mm 2 core armour cable to flat, 5 mtrs, dno supply DP isolator, there side all 25mm.
Flat has 6 way wylex with BS3036 fuses.
Took a few sockets off (metal clad) no cpc or flylead.
Ceiling roses again no cpc
Cooker no cpc.
Then seen it was wired in conduit, wondered if it was continuous. Done a quick R2 and had continuity back (yay)
Obviously we are looking at about 14th edition time of install im guessing. conduit used as cpc is fine, and i believe is still fine.
Not tried to use pipe and get new cpc to points dont know whats hidden in the concrete
my questions,
1. On my r2 test is impossible due to no cpc, so im i correct in putting N/A here and then record the R2 in its column.
2. Should i split the ring into radials, as cpc is a radial or leave as ring.
3. Anything i should mention on departures, ie the 20mm pipe as cpc.
Just looking for pointers to make sure i cover the bases with my cert.
Cheers