Looked briefly at a job this afternoon for a builder i know,as i was bouncing between jobs,

Its 2 bed flat in a high rise block. Quite old, just from quick look and see what springs out method... lol find out a lot in 15 mins hahaha, if not less.

TN-S, 6mm 2 core armour cable to flat, 5 mtrs, dno supply DP isolator, there side all 25mm.

Flat has 6 way wylex with BS3036 fuses.

Took a few sockets off (metal clad) no cpc or flylead.
Ceiling roses again no cpc
Cooker no cpc.

Then seen it was wired in conduit, wondered if it was continuous. Done a quick R2 and had continuity back (yay)

Obviously we are looking at about 14th edition time of install im guessing. conduit used as cpc is fine, and i believe is still fine.
Not tried to use pipe and get new cpc to points dont know whats hidden in the concrete

my questions,
1. On my r2 test is impossible due to no cpc, so im i correct in putting N/A here and then record the R2 in its column.
2. Should i split the ring into radials, as cpc is a radial or leave as ring.
3. Anything i should mention on departures, ie the 20mm pipe as cpc.

Just looking for pointers to make sure i cover the bases with my cert.

Cheers
 
1) I would say yes, r2 in not really applicable as you don't have an end to end reading. So, record R2 in the R2 column. 2) I would say leave. If the conduit is continuous throughout the place, it should be a really low continuity reading and capable of meeting the disconnection times and Zs for the 32 amp protective device. 3) Nothing for departures BUT, it wouldn't hurt to attach a separate document (your letter head for example) explaining these points. In the departures box, just write 'no departures, but see attached notes' It just shows that you've considered your choices carefully.
 
I had a 99% idea of what to record and what to do, but when its not clear cut, a bit of doubt creeps in. Then you have to hold your hand up and ask the questions.

My Only concern is that i have no cpc ring, so in my mindset, this isnt a true ring main final. That is why im thinking split into 2 radials only 9 doubles on it.

But as regards departures, didnt enter my head to supply a supplementary sheet explaining the use of the conduit as the circuit cpc.

Thanks for answereing
 
Agreed, but i dont want any come backs what so ever. Yes i know the regulation clearly states the conduit can be used as the cpc. Its just this world we live in. Either go the extra mile and ask questions and get it right. Or just keep posting in the general forums and encourage the diluties to kill someone. I ask here,for a reason.

I thank you all for replying its appreciative
 
Not knocking you, but seeing as it is in the regs and perfectly fine, it just seems a little weird to be asking about what to do.
 
Knocking/weird could interprit as double entendre. But i digress.....

like I said i was 99% happy in what i was going to do, but if your not 100%, then sorry i must have to get weird and post the question. Its always nice to get confirmation and input of other sparks who may have actually encountered this before,under the current regulations.
 
Knocking/weird could interprit as double entendre. But i digress.....

like I said i was 99% happy in what i was going to do, but if your not 100%, then sorry i must have to get weird and post the question. Its always nice to get confirmation and input of other sparks who may have actually encountered this before,under the current regulations.
I don't think there is anything wrong with asking something that others may find basic. When you work on your own you don't necessarily have anyone you can bounce ideas off, so the forum is very good for that. Sometimes it's easy to over think things too, so even if it's a case of being told that - it all helps. Also at the end of the day you are clearly trying to do the best job you can and credit to you for that. Even if you don't 'have' to include additional notes, if it makes you feel that your being more thorough and that you've covered yourself - then go for it I say.
 
Its all gravy. Double checked with Niceic this morning, they reminded me what i needed to fill the cert in correctly.

As regards departures i should have said comments on existing installation, of which they said i should put the comment in there about the conduit.

r2 i would enter con, and record R2 as measured.

Its all clear now, so thanks for stopping by, those that did, cheers
 