Hi all.

Although I'm not doing the work this is something that's bothering me with the ongoing works so I though I'd ask for advice.

I'm in the process of fitting a new Kitchen / Washroom / Bathroom and have come across the re-wire work done a few years ago to fit a new MCU with long meter tails ( 5 mts ) from the main fuse.

The meter tails have been run in plastic low smoke 20mm Kopex Plastic tubing ( sort of stuff we use in the comms industry for Fiber optic cable protection), and is twin cable with a separate earth cable. The meter tails are 16mm and the separate earth is 10mm all contained in 20mm Kopex.

Is this a correct install or does this need to come out and be replaced by T&E armored..?

It is routed through ceiling joists in at least 3 places.

Any advice anyone before I call in help.

Thanks........:stooge_moe:
 
When you say 'meter tails' are you stating the cables coming from the meter to your CU are T&E? Or is there an isolator supplying your CU
 
When you say 'meter tails' are you stating the cables coming from the meter to your CU are T&E? Or is there an isolator supplying your CU

It's the tails from beyond the meter. The old MCU has been relocated from 1mt above the meter to 5mts further into the house.

Sorry, didn't make that bit clear
 
3 metres is the limit

Cheers. Anyway I can get this resolved. I have seen quotes of getting a 80amp switch fitted within 3 meters of the meter then on to the new MCU ( Which with the Meter's location would not be a problem ) or do I have to get a new supply into the house form outside into the new MCU ( Lots of work and costs )

Sorry, it's just for advice chaps..

Thanks
 
Youre talking about a sub main here, with a switch fuse as you said , I wouldn't get a new supply , it's not needed and would cost a fortune
 
You need to fuse down the tails to protect them if they are over 3 metres putting in a switch will not change things you could you a switch fuse for convenience.
 
Youre talking about a sub main here, with a switch fuse as you said , I wouldn't get a new supply , it's not needed and would cost a fortune

Cheers Ray and all so far.

OK, Yes it would be a sub main.

On the installation, is as described above acceptable or does this need replacing with 16mm T&E armored (Not at this stage and impossible job).

Sorry, we're on a tight build schedule so it's advice only at this stage.
 
just fit a 80A switch fuse after the meter. that 16mm will happily handle 80A. if it ain't broke..... don't fix it.
 