Unless i`ve misunderstood your original post, did you not state the sub to the stable is 30mA protected? Obviously you`ll rectify this when you put in the new feed, yes?
Unless i`ve misunderstood your original post, did you not state the sub to the stable is 30mA protected? Obviously you`ll rectify this when you put in the new feed, yes?
Hi
The house seems already loaded and if you add this supply to it you may overload the supply putting the house in jeopardy , your also installing a system that does not allow expansion for both the house installation and the stable installation. You don't need the 100mA type s if your enclouse is non conductive and your tails are very short in length. Protection of final circuits as per TT system.
Regards
Hi
100mA is for final circuits, not as a main switch, I would use 300mA so you get some discrimination between the personal protection RCD's (30mA & 100mA). I would only install the 100mA if the TT installation doesn't go well and you end up with a high ze even then I would bang another rod in.
Regards


Client may not want conduit but where horses are involved metal conduit is the best idea, should they say no, say to them horses can chew through cable but not metal conduit and which do they value more the cost of horses or the cost of installation
Remember when doing 2391-20 Design course a previous exam paper was a stables and it was required to be done in metal conduit because of the horses.
Another thing to remember is if somthing happens to one of the horses becauseof your installation make sure your insurance is up to date.