Yep, this is a standard requirement for sub-station rooms/buildings. Never, ever seen this done in aluminium though. That is possibly going to create more problems than it's initial cost reduction!!
Normally the two ends of this room loop would connect to a MET/MET earth bar, with removable links to facilitate testing. One section of the earth bar would connect all the earthing conductors, such as earth rods, Ufer earth mat, etc, and a second section would contain electrical links from cables TX, switch boards etc. The tape would be used to locally connect and equalise other metal structures or componants within the room, like the metal doors, windows (if any) ventilation louvers and other metallic plant, like AC units and/or it's ducting etc....
We're hoping to have a few more of these of the back of this then doing them quite regular if everything goes ok. Will be interesting to see if the other ones we do are aluminium or copper tapes.