Got an EICR to do tomorrow so just getting a headstart on paperwork .. customers sent me a few pics , straight away fuse board is OAF .. no RCD ... Now .. how do I code this ? And what's your thought process ..
I have it in my head that , should a customer be able to run an extension lead out...
Hey all , customer rang last night, full house tripping .. can I come out ( after hours ) ... Got there for 6pm .. ran tests and discovered a dead short on the upstairs lights ... Went in to attic to discover what I can only describe as SPEAKER CABLE wiring up a lighting circuit consisting of 6...
Hey guys , went to a job last night to quote for a new shower install ... After removing the old shower front , I discovered 2 X 2.5mm t&e instead of 1 6mm .. the current shower is 8.5kw and ran into a 40a MCB on RCD side of a split board .. no signs of perished cables or burning anywhere ...
Hey guys .. I'm running a new circuit to a large outside area in a garden , consisting of 5 heat lamps 250w each ...
I've done the calcs and it will.be pulling 5a . Cable run is only 15m
Are there regs on outside heater lamps in the 18th ?
And
Would 2.5 armoured on a 6amp MCB be ok ...
Thanks for advice ... I was told the shower had been replaced to rectify the same fault .. but it's still happening .. so I've ruled the shower unit out ... I will report back later on and see if I've resolved the issue
He f
Hey guys , just been to a fault finding job and discovered what I think may be the problem but the consumer unit may be overloaded , please advise on the following ...
The shower circuit is on a 32a MCB (wrong should be 40a) which I think is causing the tripping of the rcd , my dilemma is that...
Would I need it to be a 4 core and earth ? To include the neutral .. ? .. as 3 core is ,grey common .. black L1 brown L2 ... Appreciate the advice .. thanks ..
I spent the best part of an hour thinking I'd messed up the 2 way switching and called it a day .. come back Monday with a fresh head ... But upon leaving .. I assumed I'd missed a neutral , so no .. didn't check ... Still learning boys .. I'll report back Monday ... Ps... Can I nick a neutral...
Ive left the job now .. but 1st gang was fine for the spots ... I linked over to second gang for 2 way switch for batton ... But batton will not come on .. power is at the second switch and also at the batton ... I think there's no neutral at the batton ... Hope this makes sense ..