Hey guys , just been to a fault finding job and discovered what I think may be the problem but the consumer unit may be overloaded , please advise on the following ...

The shower circuit is on a 32a MCB (wrong should be 40a) which I think is causing the tripping of the rcd , my dilemma is that in its current state the consumer unit is loaded up with 3 32a and 1 16a circuits adding up to 116a ... Is this overloaded ? do you apply diversity to consumer unit ? I've done all my tests on shower circuit which is on a 6mm2 cable and all is fine .. am I safe to replace 32a MCB to 40a MCB ? ... Thanks for any help
 
Hey guys , just been to a fault finding job and discovered what I think may be the problem but the consumer unit may be overloaded , please advise on the following ...

The shower circuit is on a 32a MCB (wrong should be 40a) which I think is causing the tripping of the rcd , my dilemma is that in its current state the consumer unit is loaded up with 3 32a and 1 16a circuits adding up to 116a ... Is this overloaded ? do you apply diversity to consumer unit ? I've done all my tests on shower circuit which is on a 6mm2 cable and all is fine .. am I safe to replace 32a MCB to 40a MCB ? ... Thanks for any help
What brings you to believe that an undersized CB causes the RCD to trip? You don't just add up the CB sizes, apply diversity to the circuits.
Was this not covered on your DI Course?
 
1. if the MCB for the shower were undersized, then it would trip, not the RCD,
2. rule if thumb with CU load ... add up MCBs and x 0.4.to get an approximation of the actual load (diversity).
3. IR test each circuit for leakage or ramp test RCD with all circuits connected (main switch off). then with circuits dissed from RCD, it there's an appreciable difference, that's your leakage.
 
Because all my tests and checks lead to the under rated CB ... The shower is newly installed so it's not the shower so to speak
that's like thinking your brakes have seized when the clutch is slipping. you're being led down the garden path.
 
Because all my tests and checks lead to the under rated CB ... The shower is newly installed so it's not the shower so to speak
If it was proved that the cb was indeed underrated, it would surely be the cb that eventually tripped and NOT the RCD, RCDs trip usually on a fault to E, NOT on an overload as you seem to have suggested. Why could it not be the Shower that's at fault? As Tel suggests IR test the wiring again, after dissing it from the CU first of course, might not be the Shower, could be the wiring that's iffy.
 
Last edited:
Thanks for advice ... I was told the shower had been replaced to rectify the same fault .. but it's still happening .. so I've ruled the shower unit out ... I will report back later on and see if I've resolved the issue
If it was proved that the cb was indeed underrated, it would surely be the cb that eventually tripped and NOT the RCD, RCDs trip usually on a fault to E, NOT on an overload as you seem to have suggested. Why could it not be the Shower that's at fault? As Tel suggests IR test the wiring, dissing it from the CU first of course, might not be the Shower, could be the wiring that's iffy.
He f
 
Thanks for advice ... I was told the shower had been replaced to rectify the same fault .. but it's still happening .. so I've ruled the shower unit out ... I will report back later on and see if I've resolved the issue

He f
Look forward to your answers
 
don't forget that the 32\A MCB type B will run at 50A fir about 17 minutes. plenty of time to get wet and clean
 
Last edited:
Looks like a clear head and some logical fault finding saved the day.
well done and thanks for getting back to us with an update, its nice to know how these things turn out.
 

Reply to Tripping shower (fault finding) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
1K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
668
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
1K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock