Got an EICR to do tomorrow so just getting a headstart on paperwork .. customers sent me a few pics , straight away fuse board is OAF .. no RCD ... Now .. how do I code this ? And what's your thought process ..

I have it in my head that , should a customer be able to run an extension lead out the door /window of the house and use a Jetwash or any other equipment .. I regard this as "potential danger" C2 ? ...

Most would say C3 and I agree In some respect

.. Napit Codebreakers book is great but not 100% clear on the situation ... Any train of thought would be nice thanks
 
No point mincing about these days imo

if it ain’t got any rcd on the installation then i Strongly recommend a board change before even bothering spending 4 hours doing an eicr which ultimately will just fail due to lack of any rcd protection
 
Got an EICR to do tomorrow so just getting a headstart on paperwork .. customers sent me a few pics , straight away fuse board is OAF .. no RCD ... Now .. how do I code this ? And what's your thought process ..

I have it in my head that , should a customer be able to run an extension lead out the door /window of the house and use a Jetwash or any other equipment .. I regard this as "potential danger" C2 ? ...

Most would say C3 and I agree In some respect

.. Napit Codebreakers book is great but not 100% clear on the situation ... Any train of thought would be nice thanks
I personally look at the condition of the installation, if class 1 accessories, electric shower fitted, outside lighting etc its a C2 for me personally. Boards and Installations can be OAF and still be serviceable and safe.
 

Reply to No RCD !! C2 or C3 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Just had an EICR done and C2 (dangerous) applied to 3-way consumer unit which is exclusively for 3 x Storage Heaters. Pic below. Yes its plastic...
Replies
24
Views
2K
Hi, I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican...
Replies
59
Views
6K
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
Fun EICR at an HMO today, which was installed new 5 years ago (not particularly well!) Lots of niggly things that I'll sort, but in the kitchen...
Replies
61
Views
5K
Did a couple of inspections on 2 x 2 bed ground floor flood damaged flats today, only 4 circuits in each, bizarrely one socket circuit and 2...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock