Barrington1990

Got an EICR to do tomorrow so just getting a headstart on paperwork .. customers sent me a few pics , straight away fuse board is OAF .. no RCD ... Now .. how do I code this ? And what's your thought process ..

I have it in my head that , should a customer be able to run an extension lead out the door /window of the house and use a Jetwash or any other equipment .. I regard this as "potential danger" C2 ? ...

Most would say C3 and I agree In some respect

.. Napit Codebreakers book is great but not 100% clear on the situation ... Any train of thought would be nice thanks
 
also a C2 for bathroom circuits if no RCD or supplemantary bonding present. newboard required. .
 
  • Agree
  • Like
Reactions: e-spark and loz2754
No point mincing about these days imo

if it ain’t got any rcd on the installation then i Strongly recommend a board change before even bothering spending 4 hours doing an eicr which ultimately will just fail due to lack of any rcd protection
 
  • Agree
Reactions: loz2754
Got an EICR to do tomorrow so just getting a headstart on paperwork .. customers sent me a few pics , straight away fuse board is OAF .. no RCD ... Now .. how do I code this ? And what's your thought process ..

I have it in my head that , should a customer be able to run an extension lead out the door /window of the house and use a Jetwash or any other equipment .. I regard this as "potential danger" C2 ? ...

Most would say C3 and I agree In some respect

.. Napit Codebreakers book is great but not 100% clear on the situation ... Any train of thought would be nice thanks
I personally look at the condition of the installation, if class 1 accessories, electric shower fitted, outside lighting etc its a C2 for me personally. Boards and Installations can be OAF and still be serviceable and safe.
 
  • Like
Reactions: loz2754

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
No RCD !! C2 or C3
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
6

Thread Tags

Tags Tags
no rcd rcd

Advert

Thread statistics

Created
Barrington1990,
Last reply from
timhoward,
Replies
6
Views
2,467

Advert