Today my 3 bed room 7 year old rental property got EICR inspected, the result says unsatisfactory due to No CO alarm and heat alaram in kitchen. Also, the Firalarm device expired in January. All are battery-operated, so I asked if I could buy and install one. He mentioned that if I do it myself, we have to conduct an EICR again. If I take their service, we will amend the report after the remedial work is completed.

So my equation is why they do not allow me to change, also why they are checking CO and heat alarm as it is nothing to do with electrical installation.
 
You are right. The smoke and Co detection are not part of an EICR unless they are mains powered.

The state of the detectors, ie, within date or whether they’re there or not, may be included in the report, but just to bring attention to the owner as a general safety observation.

It would not make the report unsatisfactory.
 
To be perfectly honest... for a 7 year old property, these things should have been there from day 1, and be all mains powered.

Smoke and heat detectors should have a 10 year date... so did they used old 3 year old stock when the built the house, or is it older than you were led to believe?

Are you the tenant or the landlord?
 
To be perfectly honest... for a 7 year old property, these things should have been there from day 1, and be all mains powered.

Smoke and heat detectors should have a 10 year date... so did they used old 3 year old stock when the built the house, or is it older than you were led to believe?

Are you the tenant or the landlord?
To be perfectly honest... for a 7 year old property, these things should have been there from day 1, and be all mains powered.

Smoke and heat detectors should have a 10 year date... so did they used old 3 year old stock when the built the house, or is it older than you were led to believe?

Are you the tenant or the landlord?
landloard
 
You are right. The smoke and Co detection are not part of an EICR unless they are mains powered.

The state of the detectors, ie, within date or whether they’re there or not, may be included in the report, but just to bring attention to the owner as a general safety observation.

It would not make the report unsatisfactory.
Only the Fire alarm is weird, the other CO and heat alarm I can buy battery-operated
 
2016? so 9 years old, not 7.

2.5 hours doesnt seem enough time for a 3 bed... although a relatively new build shouldnt throw up any surprises. It could be possible if hes well practiced.

Is it possible for you to post up the pages of the report with all personal details of your property address and their company name redacted?
 
You are right. The smoke and Co detection are not part of an EICR unless they are mains powered.
BS7671 reg 560.10 makes no reference to mains or battery
The state of the detectors, ie, within date or whether they’re there or not, may be included in the report, but just to bring attention to the owner as a general safety observation.

It would not make the report unsatisfactory.
I attended an Aico event a few years ago where the FIA (Fire Industry Association) gave a presentation on this subject and given an EICR is an inspection for compliance with BS 7671 and if there are compliance issues with BS5839 then BS7671 reg 560.10 cannot be complied with and therefore the EICR could be unsatisfactory

The issue I see is that given all the changes to the fire detection and CO detection requirements in the last few years especially in the rented sector there may be a need to upgrade the current fire and CO detection to meet the current requirements which may mean mains / battery powered detectors depending on the property
 
If what you say is true,UNG,then it would merit a C3 surely? You would be advising the client that the smoke detectors are out of date and need replacing.I cannot see how they could be a C2.Seeing as there's no mention on the EICR certificate of smoke detectors then I cannot see how it could warrant a fail.A mention,yes, but a fail no.
 
If what you say is true,UNG,then it would merit a C3 surely? You would be advising the client that the smoke detectors are out of date and need replacing.I cannot see how they could be a C2.
If detectors have passed the expiry date are not fitted correctly or are the wrong type why would it not be a C2, as mentioned previously the fire and CO regulations are constantly changing and also vary from each country in the UK . For me this is always a grey area in the rented legislation you have to have a gas cert, you have to have an EICR yet there is no actual annual certification requirement and the only maintenance requirement for the fire detection equipment is the weekly or monthly checks and tests by the tennant
Seeing as there's no mention on the EICR certificate of smoke detectors then I cannot see how it could warrant a fail.A mention,yes, but a fail no.
I suppose a lot depends on the EICR sheet you are using mine has
1752517368965.png
I always include fire, CO and any other items not covered previously in this section on my certs
 
The online NIC/EIC forms do not have this section as far as I can see.
Thanks, Bob. From the above discussion, it seems it is a gray area. How come the landlord knows all of this? Also, the electrician should allow the replacement as DIY. However, the electrician said that if I do it myself, he will have to re-conduct the test for the entire house. If that is the case, why is the vendor selling smoke detectors to everyone? It should be strictly for electricians only. I feel something is not right. Moreover, my current EICR is expiring end of the month and council landlord licensing will impact compliance. Moreover, they do not have time to do remedial work (fire alarm, CO, heat detector).
 
Ask for a Regulation number.
I agree with you, though I suppose an argument could be made that 110.1.3 and 560.10 bring it within the scope of BS 7671.

Personally I feel a comment is more appropriate for this type of thing though as opposed to a coded observation as it is a different standard being applied.
 