I dont have much experience with this stuff but have recently completed an install and an issue has arisen. Maybe you guys can give me an answer.
The scenario is we installed cableing,LED lighting and connected all to drivers and PSU's supplied by the lighting designer,all of these are located on a central board in a roof void. Another company installed lutron control panels and commisioned the system.
Some of the lighting is dimmed and some are on straight switching outputs. Just after commisioning one of the PSU's supplying LED tapes failed,as there were no obvious issues I put it down to a dodgy unit and asked the lighting designer to supply another. Replaced the offending PSU today only for it to go up in smoke..(literally) within minutes of starting.
Too much of a coincidence, I checked the obvious connected load...no probs...and IR tested the cableing...no probs either.
It didnt take long to discover that the lutron comissioners had programmed this circuit as a dimmed output,and it was dimmed...it should have been a straight on/off. Now the PSU is a 60w 24v non dimmable unit,but it states on the case that the input voltage is 100-230v.
I called the manufacturers tech line to see if connecting this unit to a dimmed supply would cock it up,but couldnt get a definate answer...My problem is as follows,
As this is the only PSU to have failed on the system...(twice),and is the only circuit to have been incorrectly programmed....I blame the comissioners and have asked them to pay for the additional two PSU's..which are not cheap.....They are not having it and say they are not responsible.
They are going to reprogram the panel...but I need a definate answer on whether the PSU failure can be attributed to it being dimmed...as someone is having to pay,and it's not going to be us!
The scenario is we installed cableing,LED lighting and connected all to drivers and PSU's supplied by the lighting designer,all of these are located on a central board in a roof void. Another company installed lutron control panels and commisioned the system.
Some of the lighting is dimmed and some are on straight switching outputs. Just after commisioning one of the PSU's supplying LED tapes failed,as there were no obvious issues I put it down to a dodgy unit and asked the lighting designer to supply another. Replaced the offending PSU today only for it to go up in smoke..(literally) within minutes of starting.
Too much of a coincidence, I checked the obvious connected load...no probs...and IR tested the cableing...no probs either.
It didnt take long to discover that the lutron comissioners had programmed this circuit as a dimmed output,and it was dimmed...it should have been a straight on/off. Now the PSU is a 60w 24v non dimmable unit,but it states on the case that the input voltage is 100-230v.
I called the manufacturers tech line to see if connecting this unit to a dimmed supply would cock it up,but couldnt get a definate answer...My problem is as follows,
As this is the only PSU to have failed on the system...(twice),and is the only circuit to have been incorrectly programmed....I blame the comissioners and have asked them to pay for the additional two PSU's..which are not cheap.....They are not having it and say they are not responsible.
They are going to reprogram the panel...but I need a definate answer on whether the PSU failure can be attributed to it being dimmed...as someone is having to pay,and it's not going to be us!