Current carrying capacity is a figure which is given to us by manufacturers, correct? Now, I've watched those videos of the guy trying to set fire to a piece of 1mm and it takes quite a bit more current to set a light. So for example, if you had a 9kw shower and a 9.5kw instantaneous unvented...
Hi All
I would like some opinions from fellow sparks,I work as a foreman electrician for a large Logistics company and I am part of the building maintenance team we have all trades in the team. Each depot has a what my Manager calls maintenance men ( I call them caretakers/Janitors), they carry...
thebassman
Thread
carrying
company
electric
electrical
electrical work
led
out
persons
within
evening all working away with no regs etc anyone tell me cable size for 200a 3ph head feeding a 6way 3ph ryfield board singles direct from head to db approx. 1m long cheers
Hello, I was just looking for some help with the above subject with looking up the tables for the various protective device and finding the values of C connected with CCCC. I was looking for the rating factor for a BS88 fuse and I found at least 2 different tables the difference being that there...
Hi, looking through an EICR report and have a issue with the MDP.
We have
4x240 - on a 1440 breaker
3x240 - on a 1250 breaker
2x240 - on a 630 breaker
All cables are ducted within the ground. Am i right in thinking that there are breakers are over rated for the cable size. Just double...
EICR
tnc-s system ....lighting circuit ......cables buried less than 50mm ....not rcd protected....what code should i put
(i think code 2...
but could it be c3 (not compliant with current regs)
Why is it that the tables in the Regs for Cable current carrying capacities vary so much from that of a cable manufacturers data sheet, for example a table in the Regs book states a 240mm 4 core XLPE Armoured cable buried will carry 324 amps, but a data sheet for a leading manufacturer states...
Tonkolili
Thread
cable
capacity
carrying
current
current carrying capacity
can anyone help please,
I am testing a new installation for another contractor, lighting circuits are wired in 1.5mm pvc singles in 4inch metal trunking, protected by 16amp type c mcbs, is this overated considering correction factors applied? thanks
Coming across this more often, situation, 200a bs88 main switch, feeding busbar above. 3 dbs next to busbar, all single phase, supply to these is 16mm tails off busbar. Now my issue is 16mm tails cannot take 200a,so C2. But on the previous EICR they said that because the db was less than 3...
Any reason why 6x1.5 mm singles within 20mm plastic cinduit on surface shouldnt be used for a 3kw load. Length if run is about 6 metres. Fused a 13a via sf spur.
Thanks
goldie
Thread
capacity
carrying
current
current carrying capacity
Does the current carrying capacity of cables change on what voltage your using??
2.5mm can carry 27a at 230v
would this be the same for 1000v
could someone please explaain this whole process please
Confused lol
Grant
p.s i'm a student :)
iamgary25
Thread
cables
capacity
carrying
current
current carrying capacity
different
power
voltage
voltages
volts
Can anyone help me out with this? Need to find the max current carrying capacity for 4mm singles over a 10m length in both metal trunking/pipe with a 20A 60898 B Type breaker protecting cct. No thermal insulation at an ambient temp of 30•C.
If anyone can help with breakdown of calculations...
markjenks
Thread
capacity
carrying
current
current carrying capacity
Hi all
Been around for a few weeks but this is my first post so thought I would say hello
just after some advice from some sparks in Scotland. I use to work for a large NIC firm in England doing installation and periodic inspections. I know you have to be registered with a scheme to comply...
Hi all
Been on Doncaster website and can not find the capacity for a 2.5mm 2core firesure. I am assuming this is because the match the installation methods of a T+E.
does any one have the relevant info.
Cheers Beaver
HI...
Would i right in saying that it is important to first check that a property is earthed sufficiently and that readings are within what they should be for T-N-C-S, T-N-S, TT systems.
Upon discovering a house has no main earth route back to star point would it be correct to say that no work...
jamesBoater
Thread
before
carrying
earth
earthing
electrical work
fault
james
out
property
In the red Osg is t&e table 6f ? Ie flat cable? I notice that table 6 e1 has two core and three core non armoured would this cover t&e or is this for flex only.
We havnt covered this in college
Thanks for any help given.
Craig.
Patto
Thread
capacity
carrying
current
current carrying capacity