hi

I've been asked to pick up a job where the previous builder went into liquidation and the property management company is asking me to complete the electrical works, relocate a fuseboard.

Everything the previous company has done is exceptionally neat but I'm concerned on the design front with the SWA, the supply from the mccb panel is 100A and the new swa they have pulled in is 16mm 4c (TPN) looking at the guides on the web current carrying capacity for this clipped direct is 94A, struggling to remember the exact formula would have to go through the books but is the 94A a guide and you can calculate it exactly?

Would rather not derate the mccb, and it's virtually impossible to rewire without taking ceilings down

Thanks
 
Hi - worst case is 3phase 70C rated then 16mm clipped direct is 77A, but if you are only using single phase of the cable it's 89A. If the cable is 90C rated then its 94A and 110A respectively. Hope that helps :)
 
What your mac demand looking like taking diversity into account.? Id go with others and say derrating the mccb may be the way forward if the install could work off lower rated mccb
 
To be honest I wasn't aware you could just wind it down, having researched them a little I understand there is a pot on them which allows you to adjust the current setting

Thanks
 
To be honest I wasn't aware you could just wind it down, having researched them a little I understand there is a pot on them which allows you to adjust the current setting

Thanks

Then I'd suggest getting the advice of someone who knows what they are doing, there's usually adjustments on both magnetic and thermal tripping characteristics. You're outside the territory of plug and play fixed protection now.
 
Then I'd suggest getting the advice of someone who knows what they are doing, there's usually adjustments on both magnetic and thermal tripping characteristics. You're outside the territory of plug and play fixed protection now.

I see by your wonderful post that teaching people new things just isn't your style...
 
It's a strange setup this, I'm doing the work on behalf in the managing agent so only looking at landlords side, there is another sparks working for the fit out company and for some strange reason they didn't want him to take on all the works.

I wanted to pull the cables back through the galvtrunking on the 2nd floor and get a hole through the floor (builders works) dropping into the board in copex, told no holes through the floor.

So we ran 24 circuits through the first floor, up the riser to the existing db location for a junction box, din rail connectors

Literally about to start stripping out the db ready for the junction box to be told that there is no room for a junction box in the riser and I should have pulled the cables back through the 2nd floor, ffs!

Fortunately client is on my side this route was discussed and agreed but I've got to pull it all out and start again.

In the new db the other sparks was intending on fitting a meter, I have now found out the 16mm swa is a sub main off another board hence the meter, the meter looks like it needs a connection for power but I'm not sure where to connect it, are they fuses on the bottom right and I need to come off the main switch?

View attachment 35397
 
It's a strange setup this, I'm doing the work on behalf in the managing agent so only looking at landlords side, there is another sparks working for the fit out company and for some strange reason they didn't want him to take on all the works.

I wanted to pull the cables back through the galvtrunking on the 2nd floor and get a hole through the floor (builders works) dropping into the board in copex, told no holes through the floor.

So we ran 24 circuits through the first floor, up the riser to the existing db location for a junction box, din rail connectors

Literally about to start stripping out the db ready for the junction box to be told that there is no room for a junction box in the riser and I should have pulled the cables back through the 2nd floor, ffs!

Fortunately client is on my side this route was discussed and agreed but I've got to pull it all out and start again.

In the new db the other sparks was intending on fitting a meter, I have now found out the 16mm swa is a sub main off another board hence the meter, the meter looks like it needs a connection for power but I'm not sure where to connect it, are they fuses on the bottom right and I need to come off the main switch?

View attachment 35397

Sounds like a right pain in the backside job mate.
 
Sounds like a right pain in the backside job mate.

It is, wish I never got involved, I've had to connect the swa to a temp board for now, when they fit the new board they will re terminate my swa, I could pull 3 circuits back through the first floor but I'm not touching the 2nd floor without another order, will test what I've done and close the job as far as I'm concerned, once they've argued it I'll go back and change it, means this will get stripped out though

View attachment 35398
 
hi

I've been asked to pick up a job where the previous builder went into liquidation and the property management company is asking me to complete the electrical works, relocate a fuseboard.

Everything the previous company has done is exceptionally neat but I'm concerned on the design front with the SWA, the supply from the mccb panel is 100A and the new swa they have pulled in is 16mm 4c (TPN) looking at the guides on the web current carrying capacity for this clipped direct is 94A, struggling to remember the exact formula would have to go through the books but is the 94A a guide and you can calculate it exactly?

Would rather not derate the mccb, and it's virtually impossible to rewire without taking ceilings down

Thanks

Hi, id suggest probably okay, the designer may have tweaked the factors applied to the cable ccc, if so you can get it above the 100 amp.
 

Reply to Swa current carrying capacity in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, go easy on me please, I've just returned to the trade, well I am about to, I received my Gold Card last Thursday. I've been gen'ing up for a...
Replies
4
Views
847
Had UKPN come out to a property recently to upgrade the main fuse from 60A to 100A but when they arrived they said that the supply cable which he...
Replies
9
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
407
I have a 37KW motor and need to replace some burnt out 35mm2 tri rated cable(loose connection). I’ve looked at 25mm2 Tri rated cable the data...
Replies
6
Views
3K
A builder has asked for a quote for rewiring a domestic property all very straight forward until he mentioned relocating the consumer unit to...
Replies
16
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock