as title says, just doing an EICR and cu has MK switchgear, the BS number is not available in NICEIC dropdown box and cant insert it manually either.
any ideas ?
picture attached
I wonder if anyone can suggest a scenario that could have made this happen.
I did a full rewire on a two bed purpose-built flat a few weeks ago. TNCS, cut-out in cupboard at the stair-well, I ran the tails to a switched fuse inside the flat and on from there to the consumer unit.
All tested...
My shed is only 5 Meters from my house, i will run a SWA cable from existing consumer unit to a shed consumer unit which will have 3 circuits for Sockets,Light and a 7.5Kw shower unit all i need to know is will a 16 Amp MCB be sufficient for the socket Radial circuit for 4 Double sockets
Please, help me to find the brand and model for a 120Ac 60 amp circuit breaker that can be remotely, turned on, off, and trip reset. It is used in the output of a small 7KVA gasoline generator.
I found online the “Smart Breakers WiFi” from Leviton; but there is no WiFi on the yacht, and I don’t...
Seen a consumer unit hager today, was old, the mcb had a little door on it, I opened one and it had a 3a plug fuse in it. Are they for storing stuff. Whats the low down with them? Cheers.
Initially was obviously a hard fault because mcb would not reset. Unscrewed and checked all light switches for obvious fault (some metal) no visual problem, then found possible issue with disconnected wire in ceiling. Rose. Repaired this and initially mcb stayed in. Connected each light switch...
I want to check the rules when doing an EICR for MCB size for ovens. My mate says i should fail an installation because there is a 40 amp MCB on an oven rather than a 32 amp. Is he right?
Simple job, swap an MCB to an RCBO on a lighting circuit. It's got me totally stumped!
IR test L+N -> E is fine on the circuit. So is Zs. All 2-way switches operated.
Instant trip when changed to RCBO though, and tried two RCBO's
Ramp tested them both, all good. All tests pass on them with no...
We have a Electrical PLC Control Panel that has to supply 45 Fused Spur units, do I need to protect these with an RCD, we have a 10A Type D MCB at the moment.
Each Fused spur controls an electronic Volume/Pressure controller which is rated at 130mA.
Hi all, looking for some input from you guys. Had a call out a few days ago where someone has has a shock from brass light switch in a domestic property. When i got there, a decorator told me that he had the switch loose from the wall to strip the wall paper. He's used a steamer, so it points to...
Im looking to put a supply out in a mancave, the earthing arrangement is tns. At the supply there is iscos installed so I was going to take a supply out of the iscos into a 40 amp DP MCB and run a 6mm T+E surface piped along an outside wall. I will be installing a 40A 30mA RCD in the mancave. My...
Hello guys, completely forgot to remove the board cover to check what type of rcbo was required for this particular Crabtree board. Anyone from experience know which type RCBO fits?
thanks in advance!!
hi all. A friend asked if i would look at his kitchen sockets as they would trip just the mcb now and then. i said ill look but thats it as he had a electrician install 3 spurs and add 1 socket on a radial circuit 16amp mcb and looks like 6mm t&e from mb for the circuit and looks like the combi...
Hi folks, I’m looking for some advice on a minor problem my parents have with their kitchen lights. They have 2 light fittings in the kitchen each carrying 4 spots and on occasion when one of the bulbs go the circuit breaker trips - there are no RCDs. It only happens in the kitchen (the...
Just been to another one of those !!
Plumber replaces shower for upgraded version. 40A mcb replaces 32A. No problem mate !! that will work fine.
So 12 months later the owners girlfriend moves in with him.
So that poor old 6mm that was just starting to break a sweat for 12 months, suddenly...
Hi all,
Had my downstairs ring final circuit trip the B32 MCB today. The missus was in the kitchen cooking and had apparently put the kettle on and as it was close to boiling the MCB tripped.
I therefore assumed it would be due to the kettle so I checked the 13A fuse in the kettle plug but it...
I’ve a fuseboard as pictured, which has been nuisance tripping on the downstairs ring final circuit. It started off with 32a breaker tripping which is RCD protected, and now it’s tripping the Main RCD switch.
This is a relative's property and he’s already had an electrician in, who’s ran a...
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc