hi all. A friend asked if i would look at his kitchen sockets as they would trip just the mcb now and then. i said ill look but thats it as he had a electrician install 3 spurs and add 1 socket on a radial circuit 16amp mcb and looks like 6mm t&e from mb for the circuit and looks like the combi boiler is on the same circuit (guessing spured). Here's where my problem is he has under counter fridge/freezer, tumble drier, dishwasher, washing machine, plus all the other kitchen stuff. From my under standing from what i remember the load is to much for the 6mm cable and the 16amp mcb.
I believe hes spoke with the electrician and hes said everything is fine with it.
any advise on this would be great
thanks
 
Electrical2Go - Online Electrical Supplier
This official sponsor may provide discounts for members

buzzlightyear

-
Esteemed
Arms
Reaction score
6,244
your friend needs to get the spark back
and see what's is tripping the mcb, are there a RCD In the consumer unit.
 

Jaco13579

DIY
Reaction score
0
your friend needs to get the spark back
and see what's is tripping the mcb, are there a RCD In the consumer unit.
yes it has RCD. and will let him know to get him back. and sorry im just asking if this is right for a 16amp radial or should it be a final ring with the load that can be put on it. As i didnt think to much of the work that was done
 

pc1966

Esteemed
Arms
Supporter
Reaction score
4,689
thanks so my under standing he should have made it 20amp radial to take the extra load from the appliances
Probably, but it also depends on the cable's size & route as there are different maximum ratings depending on how well insulated it is thermally-speaking, and so how hot it gets carrying current.

If it is 6mm cable then it can generally do 32A no problem, but I suspect the various sockets are on 2.5mm hence could be anywhere between 13.5A max to 27A (but often 20-21A).
 

Jaco13579

DIY
Reaction score
0
Probably, but it also depends on the cable's route as there are different maximum ratings depending on how well insulated it is thermally-speaking, and so how hot it gets carrying current.
cheers i just want to make sure he gets the work done that he needs and im sure it runs about 8-10m either in the floor or wall (6mm t&e)
 

telectrix

-
Mentor
Esteemed
Arms
Reaction score
62,632
under counter fridge/freezer, tumble drier, dishwasher, washing machine, plus all the other kitchen stuff.

wat too much load for a 16A MCB, as said previously, cable capacity (and hence correct MCB rating) will depend on installation method of the 6.0mm T/E.
 