I want to check the rules when doing an EICR for MCB size for ovens. My mate says i should fail an installation because there is a 40 amp MCB on oven rather than a 32 amp. Is he right?
I'm not sure. Made no sense to me. I'll ask him tomorrow and post his reply. That's why I wanted to check the rules to see if it had something to do with the max consumption of the oven. Has anyone got a link to the rules so I can have a read?Nope, a 40A MCB on a cooker feed is not an automatic fail. Why does he say it is?
I'm not sure. Made no sense to me. I'll ask him tomorrow and post his reply. That's why I wanted to check the rules to see if it had something to do with the max consumption of the oven.
Has anyone got a link to the rules so I can have a read?
Subtle! Nice! Andre Preview would approve....Ib<In<Iz is the answer . (all the right symbols, but not necessarily in the right order. just checked. they are).