I want to check the rules when doing an EICR for MCB size for ovens. My mate says i should fail an installation because there is a 40 amp MCB on an oven rather than a 32 amp. Is he right?
 
I want to check the rules when doing an EICR for MCB size for ovens. My mate says i should fail an installation because there is a 40 amp MCB on oven rather than a 32 amp. Is he right?

Nope, a 40A MCB on a cooker feed is not an automatic fail. Why does he say it is?
 
No, he's talking ball hooks. If the cable is sufficiently sized for the CPD it can be any rating you want!
 
NB - lots of newer large range ovens with 5-6 induction hobs now require 40A and I've even seen 63A MCB's on 10mm cables
 
Nope, a 40A MCB on a cooker feed is not an automatic fail. Why does he say it is?
I'm not sure. Made no sense to me. I'll ask him tomorrow and post his reply. That's why I wanted to check the rules to see if it had something to do with the max consumption of the oven. Has anyone got a link to the rules so I can have a read?
 
I'm not sure. Made no sense to me. I'll ask him tomorrow and post his reply. That's why I wanted to check the rules to see if it had something to do with the max consumption of the oven.

Well, like any circuit, it depends on cable type, routing and device requirements
 
He said that because it’s not to regulation having a 6mm cable on a 40a MCB.

I actually found this answer below to a similar question on my builder.com (Is 6mm cable with a 40 amp MCB sufficient for a 8.5 kw electric shower? - MyBuilder - https://www.mybuilder.com/questions/v/38684/is-6mm-cable-with-a-40-amp-mcb-sufficient-for-a-85-kw-electric-shower), so it looks as though he's right.

"6mm twin and earth cable (which this almost certainly is) can be backed up by a maximum of a 32a MCB, even lower if other factors are involved. You'll need that 10mm cable and a 40a MCB unfortunately as your shower is going to draw over 32a. Whoever fitted the 40a MCB onto the 6mm cable originally was in the wrong."
 
The tabulated CCC for 6mm t&e (Clipped Direct) is 47A (Table 4D5)
There are other factors to consider and is not B&W, but its possible it is compliant!
 
he's wrong. 6mm cable ref. method C is rated up to 46A, so a 40A MCB is correct (if the shower/cooker draws > 32A but < 40A). only if cable is derated by refe.methof (insulation) does it warrant a 32A fuse, or even lessif need be.
 

Reply to MCB max load for an oven (EICR) in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
591
when installing circuits protected my mcb's , i have always used the 80% rule. eg a lighting circuits where the load won't exceed 80% of the mcb...
Replies
2
Views
821
I have an EV charger installed by a local firm. The install looks nice and tidy but with only a 2 meter run from the board you could hardly expect...
Replies
38
Views
2K
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
830
Here is my situation We have a dedicated oven circuit in our house with a 40A RCBO We have bought a dual fuel range cooker which states it has a...
Replies
0
Views
815

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock