My shed is only 5 Meters from my house, i will run a SWA cable from existing consumer unit to a shed consumer unit which will have 3 circuits for Sockets,Light and a 7.5Kw shower unit all i need to know is will a 16 Amp MCB be sufficient for the socket Radial circuit for 4 Double sockets
 
My shed is only 5 Meters from my house, i will run a SWA cable from existing consumer unit to a shed consumer unit which will have 3 circuits for Sockets,Light and a 7.5Kw shower unit all i need to know is will a 16 Amp MCB be sufficient for the socket Radial circuit for 4 Double sockets
No 16 A far to small, 7,5 KW SHOWER WILL TAKE APPROX 32 Amps on it's own, needs it's own dedicated circuit, should not be connected to a socket radial circuit. what siz cable will you be using for the radial?
 
No 16 A far to small, 7,5 KW SHOWER WILL TAKE APPROX 32 Amps on it's own, needs it's own dedicated circuit, should not be connected to a socket radial circuit. what siz cable will you be using for the radial?
I think the OP said there will be 3 circuits in the shed, and the question might have been regarding one of them, the sockets circuit.
There are bigger questions though, since a shower means a water supply, which could mean extraneous things to bond etc, and could have implications on the size of SWA used.
There are actually quite a few complex design considerations regarding earthing and bonding. I'd highly advise you to get your plans checked out by someone qualified.
For the record, this work is notifiable work under part P of building regs as you are both installing new circuits and (by the sounds of it) turning the shed into a special location.
 
I think the OP said there will be 3 circuits in the shed, and the question might have been regarding one of them, the sockets circuit.
There are bigger questions though, since a shower means a water supply, which could mean extraneous things to bond etc, and could have implications on the size of SWA used.
There are actually quite a few complex design considerations regarding earthing and bonding. I'd highly advise you to get your plans checked out by someone qualified.
For the record, this work is notifiable work under part P of building regs as you are both installing new circuits and (by the sounds of it) turning the shed into a special location.

I think the OP said there will be 3 circuits in the shed, and the question might have been regarding one of them, the sockets circuit.
There are bigger questions though, since a shower means a water supply, which could mean extraneous things to bond etc, and could have implications on the size of SWA used.
There are actually quite a few complex design considerations regarding earthing and bonding. I'd highly advise you to get your plans checked out by someone qualified.
For the record, this work is notifiable work under part P of building regs as you are both installing new circuits and (by the sounds of it) turning the shed into a special location.
miss read the OP Tim my bad
 
That’s good. I am qualified but not done electrical work for a while now so just checking. All I need to know really is the size of the MCB in the house consumer unit going to the CU in the shed
 
50AMCB 10mm cable or 63A MCB and 16mm cable. all depends on the total design load. esp with a bloody hot rain bath
The shower is the only big thing being used. It’s for dog grooming the other things will be a single strip light some trimmers and a hair dryer. Was hoping to get away with 6mm SWA as I have some left over in the shed. But I will take your advice. Thanks for the help
 
The shower is the only big thing being used. It’s for dog grooming the other things will be a single strip light some trimmers and a hair dryer. Was hoping to get away with 6mm SWA as I have some left over in the shed. But I will take your advice. Thanks for the help
What if I got a 5kw shower instead
 
even 7kW shower would be OK using a 6.0mm feed on a 40A MCB. efli being satisfied.
 
Going 10mm 3-core SWA at least makes sure you can meet any TN-C-S supply bonding requirements, usually good to 50A MCB but that depends, of course, on the supply Zs.

Also be aware that any new circuit (or CU) is notifiable work in England and Wales under part P of the building regulations. It might be safer, cheaper, and easier to get someone registered with one of the schemes (NICEIC, NAPIT, etc) to sort it out, even if you do the donkey work of digging trenches, etc, for the cable to go in.
 
bear in mind that your sockets will be limited. the shower takes upmost of the 6mm capacity. personally, I'd fit a 3kW under sink heater to activate when you turn the tap on. dog's only need warm water for grooming. anything above 45 degrees is too hot.
 
But would surely be better on some 2.5 and a bigger MCB.
Depends what it's for imo. In Europe it's quite common to see 16a and 5 sockets, and it will manage several tellies, chargers, a hoover, lamp, laptop etc.

In a shed maybe he wants to run power tools or maybe just plug in a radio?

Personally i would still do it in 2.5mm and 20a but 16a is doable.
 
Depends what it's for imo. In Europe it's quite common to see 16a and 5 sockets, and it will manage several tellies, chargers, a hoover, lamp, laptop etc.

In a shed maybe he wants to run power tools or maybe just plug in a radio?

Personally i would still do it in 2.5mm and 20a but 16a is doable.

Just wondered why you recommended 1.5mm and 16A. Seems a bit tight for 4 double sockets.
 

Reply to MCB Size for radial socket circuit. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
896
Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
710
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
595
Hi all, Curious one and hopefully some one of you could give me some advice. A customer has had a steeltech shed installed at their premises. A...
Replies
17
Views
1K
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
710

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock