Just wondered why you recommended 1.5mm and 16A. Seems a bit tight for 4 double sockets.
Especially when giving advice to someone who seems very unsure of what they're doing.
Discuss MCB Size for radial socket circuit. in the UK Electrical Forum area at ElectriciansForums.net
Just wondered why you recommended 1.5mm and 16A. Seems a bit tight for 4 double sockets.
I'm not, i'm just saying it can be done. 1.5mm and 16a will handle 8 doubles. That's how the French do it and i'm presuming their normes are safe. Electricity is electricity after all.Just wondered why you recommended 1.5mm and 16A. Seems a bit tight for 4 double sockets.
I hardly think that makes a difference. Safe is safe whether the person knows what they're doing or not and 1.5mm @ 16a will be fine for 4 sockets in a shed assuming he's not going to be running a load of bench tools off them all at the same time.Especially when giving advice to someone who seems very unsure of what they're doing.
I hardly think that makes a difference. Safe is safe whether the person knows what they're doing or not and 1.5mm @ 16a will be fine for 4 sockets in a shed assuming he's not going to be running a load of bench tools off them all at the same time.
Its for dog grooming. I would not be too surprised if it has in winter a heater, kettle and hair-dryer all on at once so would go for at least 20A 2.5mm radial.I hardly think that makes a difference. Safe is safe whether the person knows what they're doing or not and 1.5mm @ 16a will be fine for 4 sockets in a shed assuming he's not going to be running a load of bench tools off them all at the same time.
So i'm not sure what you are actually saying at all then. He doesn't know what he's doing therefore i should not answer the question he asked? Confused sorry.I didn't raise any questions about safety.
Yeah me too.Its for dog grooming. I would not be too surprised if it has in winter a heater, kettle and hair-dryer all on at once so would go for at least 20A 2.5mm radial.
So i'm not sure what you are actually saying at all then. He doesn't know what he's doing therefore i should not answer the question he asked? Confused sorry.
From the information provided by OP in this thread about what he wants to use the sockets for, 16a 1.5mm is fine. I wouldn't do it that way i would use 2.5mm and a 20a breaker but OP asked a question and i simply answered it. I also conceded already that it depends what it's going to be used for. 16a radial on 1.5mm can easily handle 'trimmers and a hair dryer'.Re-read the OP's comments prior to the point you suggested a 16A radial in 1.5T&E, then decide if sufficient information had been provided to determine whether or not such advice was appropriate.
Thanks everyone for your comments I will take on board everything that has been said. I do have 17th edition cert and part p but was done a while ago and not had much experience. I just wanted to make sure it’s safe. I will be using 6mm SWA from house to shed then 3 separate circuits for lights sockets and 3 kw water heater. What MCB would you suggest using in the house CU.From the information provided by OP in this thread about what he wants to use the sockets for, 16a 1.5mm is fine. I wouldn't do it that way i would use 2.5mm and a 20a breaker but OP asked a question and i simply answered it. I also conceded already that it depends what it's going to be used for. 16a radial on 1.5mm can easily handle 'trimmers and a hair dryer'.
The answer to OP's question about 'can i use a 16a breaker to run 4 sockets' is 'yes'.
40A MCB, assuming SWA is installed ref' method C, clipped direct with no insulation preventing heat dissipation.Thanks everyone for your comments I will take on board everything that has been said. I do have 17th edition cert and part p but was done a while ago and not had much experience. I just wanted to make sure it’s safe. I will be using 6mm SWA from house to shed then 3 separate circuits for lights sockets and 3 kw water heater. What MCB would you suggest using in the house CU.
Thank you.40A MCB, assuming SWA is installed ref' method C, clipped direct with no insulation preventing heat dissipation.
It would do.It would be preferable (to get better discrimination), to feed from a switch fuse at the house end, rather than a MCB.
I'v read through the thread and did not see any mention of RCD protection, IMO the CU in the shed should at least be supplied by an RCD from the main CU.
Only if the MCB in the CU is already RCD protected. IMO