pme

Search the forum,
  1. M

    PME to remote domestic dwelling

    Hi guys, thoughts on this would be appreciated. I have a 3 phase 100 amp PME supply, feeding 3 domestic dwelling about 80 mts away. Done cable calc and have chosen 50mm 4 core swa using armour to protect cable. In the 1st dwelling I have 3 phase metal DB feeding 3 sub mains, 1 to 1st & 2nd...
  2. J

    Which is the DNO earth block? PME

    Hi All I would be interested to hear your opinions on this situation: It's a property which used to have the electricity meter in the middle of the house, the consumer unit is still there and there is still a cut out with a 100A fuse in it, a neutral earth block and a small label that says it...
  3. dlt27

    PME Bonding help!

    More experienced help needed please. Scenario is Mains intake and MET(PME) outside the building in cupboard with KMF's (80A fuse) feeding flats via 16mmT+E. 2 flats gas meters are in cupboard at mains with 10mm bonds. 1 flat has gas meter in flat with no 10mm bond. Also no 10mm bonds to water...
  4. C

    100mA RCD Incomming NOT TT but PME

    Hi as the title suggests, I know of a Fuse Board, that has a 100mA RCD incoming However its not a TT system its a PME system, I've only been in the trade 2 years now so im still green, did it used to be the case that 100mA was the standard instead of 30mA protection for Domestic Dwellings...
  5. C

    Domestic Zs 5ohms! pme using electrode

    Hi. I have a family member who requires a new CU. She still has a rewireable fuse box and still has an ELCB. So no RCD's. Her install is a deathtrap waiting to happen from an earth faulr point of view! I replaced a socket on wall today and measured Zs. It was 5Ohms!!!! Shocking. I checked...
  6. NDG Elecs

    PME connection and stupid idiots!

    Hi, Had a little beer tokens job on way home today fitting a couple of smoke alarms. When I got there I noticed what looked to be a PME intake with no main earth going to it. Done a couple of Ze's and found the top connection in the photo was defunct, but the earth in the separate terminal...
  7. C

    Exporting PME

    I have a project to install 3 new TP distribution boards on a working commercial/industrial site. The main incoming supply is 3phase PME. The feed cables out to the new distribution boards will be a maximum of 40metres from the incoming supply and run in Swa cable (some above ground & some...
  8. HappyHippyDad

    Extending the equipotential Zone of PME installation.

    I was going to just add on to Voltz's thread but it seemed to come to a natural end but I had some questions. 1. A few experienced members say that you should not extend the (equipotential zone) EPZ of a PME system. Am I right in thinking that this is because of the possible potential between...
  9. ely_ellis

    To PME or not to PME?

    Hi, New to the forum and looking for some guidance. During an electrical test of a property it was found to have no earth connection other than to the incoming water and gas mains. Western Power were called to the property to confirm that PME was available but no terminal existed within the...
  10. driverman

    Diy pme system

    Says it all really. ohh, and the 2 x RCD's. They are connected together. no OCPD either!
  11. S

    TT system converted to PME - Earth rod query

    I've just installed two 100A isolators in a farmbuilding and the nearby house. The earthing arrangements seemed unusual. The power comes in overhead and a single cable drops into the main head. This has PME head and a label on the board stating that there is Protective Multiple Earthing. The...
  12. 1Justin

    odd "earth" cable between 2 PME heads

    I have some works at a small flat (4 properties). PME. Service head has been doubled up by DNO, so that supply cable for the second head exits the bottom and feeds the second. I find a 6mm green/yellow conductor strung between the PME break-outs of the two heads. It looks like the unusual work...
  13. D

    Exceeding max zs values on caravan site? With pme supply

    Hi all, first post on the forum and I hope you's can help me with a few questions I have. I have been asked to test a caravan site with the following details pme supply (with no individual spikes at hook up points) main 400a mccb with bolt on adjustable rcd(turned in the off position)i. I have...
  14. F

    Pme question

    While walking the dog local to some stables which were of the beaten track ,I was looking at how some of these houses got there electric supply thet were over head supply's .so I was thinking they must be tt systems but then I started noticing telegraph poles ,but electric ones with yellow signs...
  15. M

    Location of PME Links

    Hey pepes. I'm a bit new to Ryefield boards, so maybe an obvious one. While installing the Ryefield boards in the risers to feed the flats in a tower block (40 floors), we were told to remove the PME links from within the boards. Should there only be a link at the supply, as it is a PME system...
  16. Gazthesparky

    Best way to get new PME Earth connection

    On a previous thread I started a while back I needed to install a earth rod as a temp measure and it was pointed out to me that people have phoned the DNO and they came out quick and installed a PME connection so I'm just asking the best route to go to do the same. The Sanario is I'm heading...
  17. A

    Meter move tns head now tncs. Is it pme.

    The 3 phase service cut out for my block of 3 flats was recently moved. The service head used to be tns. The new service head is tncs. This has not been marked up as pme. My flat has a new 16mm earthing conductor(connection between old MET and new MET) , however the other 2 flats only...
  18. I

    PME & TNS supply in same building

    Hello all, Have been doing some work in a large building complex, the original building has a TNS supply but the large extension to the building has a seperate PME supply. At present there are no main protective bonding conductors to water/gas/oil and these services are common to both old and...
  19. A

    PME Earth supply

    Hi all - I am looking for some guidance around the MET for a PME installation. I am doing my first new build, which has had the supply installed, including meter and 100amp switch, however there is no earth wire provided? Is it the suppliers responsibility to supply the earth to a MET, or is it...
  20. N

    TT to PME problem.

    I had UK power Networks round to test whether my TT earth could be changed to PME at my house which it is now. They told me all ok and get utility supplier meter engineer to connect up. Called utility company, they said we don't do that. Just get electrician in to connect it up. I pointed out...