Hi as the title suggests,
I know of a Fuse Board, that has a 100mA RCD incoming However its not a TT system its a PME system, I've only been in the trade 2 years now so im still green, did it used to be the case that 100mA was the standard instead of 30mA protection for Domestic Dwellings?
Thanks,
Chris
Thanks,
Chris
No. A 100ma RCD offers no additional protection. it has probably been converted to PME as Jackhammer mentioned.
probably because pme was not available at the time.
Would it have been installed to protect meter tails that are chased in and < 50mm deep?
**EDIT** This is a wild guess by the way, I don't work to BS standards so I'm not very familiar with them.
Nope, that's a very recent addition to the regs and only allows 30mA protection to be used for this
I Thought so, but why? why notjust PME in the 1st place?
A lot of places had TT systems until the old overheads were replaced then PME was installed but obviously all the installations remained the same.
Or it's possible that someone didn't know what they were doing, didn't understand or thought that replacing a 30mA with a 100mA was a good way to cure nuisance tripping
Having a look around can often reveal an old copper twig sticking out the ground some where.
Although its possible for those earthing arrangements to be tagged off old lead water pipes.
Looks of horror these days, but our parents and grandparents managed to survive such ordeals all there lives and through to old age with no ill affects.
Regulations change and don't we know it, but remember our senior citizens were more concerned with German bombers rather than dodgy electrics. :)
Thanks,
Chris
Hi Chris , what type of property is it in ?
I have known on instances where a DNO will install a 100mA RCD (which then becomes the property of the consumer), where installations are very close to sub stations and have very high PFC and PSSC.
Which DNO? I've read a lot of ukpns new service design paperwork and never yet come across this.
Also I can't see what the advantage could be for a high pscc? An RCD would not do anything except perhaps melt under excessively high short circuit current
Haveing re-read Spins post and actually paid attention this time , I thought he had mentioned that it was because of a high Ze which was the reason why it had been done for the ones I have seen .
Reply to 100mA RCD Incomming NOT TT but PME in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
4K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...