  1. Mark42

    13A and 16A sockets on the same 20A radial. OK or not?

    I’ve just had a ‘robust exchange of views’ :) with a visiting engineer about the 16A sockets in my workshop. These, together with local 13A sockets, are run from radials in 2.5mm, protected by 20A RCBOs. I say it’s fine to have say a couple of 16A interlocked sockets, and lots of 13A doubles...
  2. dokkan1080

    32amp radial

    In a school today helping an approved contractor. There is a over door fan heater on a 32amp radial fed off a rotary isolator. It then goes into a bank of 3 switches that are used to control it. The swtchs are double pole rated at 20 amps. Isn't that a danger being on a 32 amp 4mm mcb
  3. I

    Radial circuit from 20A MCB

    Not sure if this is possible but just putting it out there... Current Situation Need to tidy up some of the mess in the garage from the previous owner of the house. Wires going all over the place. Additionally, all of the upstairs lights, the garage light and an external light are all radial...
  4. J

    Thoughts on overloaded radial?

    Hi all Pretty new to working for self. Got call out yesterday for a ring circuit that kept tripping rcd. I identified the faulty cable which had low 0.05 IR reading L to N. I followed this to where next point should be but on opening circuit found only one cable...not good. On closer inspection...
  5. Spike1947

    Light circuit from 16A Radial

    Hi Scenerio : a JB that feeds a couple of lights ! , (nothing else) in a small Barn Building ( storage use only ) , it is fed via a SWA 2.5mm2 from a 63A RCCB , CU via a 16A mcb ( feeding 2 double sockets ) in the main storage barn shed , there is no isolator in the small barn , I am wanting...
  6. N

    Ring or Radial

    Hi, Been out of the industry for 20 years and have found an interesting spark on YouTube who is very entertaining, he made a comment on one of his videos, Rings Vs Radials, would be interesting to see your views this in todays world.
  7. B

    Radial circuit split 2 ways

    Hi all, working with a spark today, basically dodgy wiring in kitchen junction boxes everywhere, all ripped out, now all we’re doing is a new 6mm cooker feed and radial socket circuit, basically new 2.5mm radial circuit from CU to one side of kitchen where spark I’m with has decided to put a...
  8. A

    Radial circuit help

    Hi, I went to look at job; it is a 2.5mm2 radial coming from the CU (from a 32A MCB) to two sockets and the sockets are using two appliances which are a 3.6 kW combi oven and a 2.5 kW 2 plate electric hob, what i've been told that it trips at the CU and sometimes it doesn't trip and the...
  9. J

    What tests for new radial circuit

    Job is to install one or two new sockets in a commercial premises. Possibly on a new radial circuit or an extension to ring. If extension on a ring them a Minor electrical certificate is required together with all relevant testing. However if a new radial circuit is the way a full EIC...
  10. G

    Loft conversion wiring

    Hi there I’m working on a loft conversion, just adding two small bedrooms in existing space. Would it be ok adding a radial circuit off a 16 amp MCB ? And how many sockets could I have? Thanks
  11. S

    Radial vs Ring in a standard 3 bed

    Afternoon all. I normally cable my first fixes in a standard 3/4 bed as follows: Ring up Ring down Kitchen ring. I was at a trade show the other day and got talking to a few people and they said they only use a ring in the kitchen. Radials up and down. Got me think what’s the standard? I know...
  12. D

    Radial final circuit

    Hi guys, just started rewiring my house, and noticed the sockets in the attic wired in radial instead of ring. Can I leave it in radial? There are only 2 sockets up there, unlikely there will ever be much load on it. I was thinking of wiring it 2,5mm2, (as it is now) on a 16A beaker. Any...
  13. B

    Adding Light to Power circuit.

    Adding a light to a Radial Power Circuit - the circuit is wired in 2.5mm and on a 20A MCB Now if I add a FCU to my Radial and then wire my light in 1.5mm this should be safe? But what if I don't use a FCU but wire the light with 2.5mm cable? what dangers are there.
  14. J

    What’s going on with this radial

    Called to a property which has just been sold to do an EICR The sockets down stairs including the kitchen were on a 16a 2.5 radial the issue being the Zs for the first couple of sockets were about average readings but the last few and the sockets in the kitchen went from 0.90 ohms to 1.19 ohms...
  15. B

    Electrician Jobs Radial Adding socket into radial circuit protected by 32amp RCB

    Just after a bit of advice regarding the following. First up I am not electrically qualified and know limits of what I would and would not attempt but am electrically read. The situation is that I have a radial power circuit fed from the consumer board and protected by a 32amp RCB feeding 5...
  16. C

    2.5mm Ring wired off a 4mm Radial

    Hi, I have been testing a domestic property today and when i started to look into the kitchen sockets there is a 4mm radial from the DB going to one socket on one side, the 4mm radial is cut into and JB'd and 2x2.5mm cables run out forming a ring for the other 4 sockets... Does this obey regs...
  17. Y

    Can I use a 32 amp rcbo on a radial circuit.

    Hello Is it OK to use a 32 amp rcbo on a radial Circuit. Cable size is 6mm2, cable length is about 15 m. There are 4 double plugs on the circuit. Loads are kettle 2.2 kw, washing machine max 2 kw, electric cooker 1 kw. Cheers
  18. sjhall

    4mm t&e radial circuit

    Hi Lads Do any of you guys run radial socket circuits ( with multiple points ) in 4mm ? Do you find 2 x 4mm in the back of a socket a squeeze? Only asking as I've just been passed 2 x 100m drums of 4mm off the lad doing the solar on a job I'm on for doing him a favour.... so 4mm radial...
  19. P

    Radial or Ring Final Issues

    Hi all I have just moved in and am in the process of adding some sockets. Am I right in saying that I can add to the circuit regardless of which type of circuit it is as the MCB is a 20a, obviously as long as I'm using 2.5mm t+e not speaker wire etc. I get the issues with RFC where 32a fuse...
  20. M

    RCD on radial for fused spurs?

    Hi all, Half way through an installation as a subby on someone else’s electrical contract. It’s for a church, in which they’ve asked me to run 2 radial circuits. Circuits 1 and 2 split a total of 10 fused spurs, 5 on each radial, each with a 3a fuse and on a 20a mcb. Cables are run under...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock