Hi All,

I have a very mystifying problem on a very simple circuit.

It is a new radial circuit for a garage power supply, it's wired in 2.5 T&E 16A MCB 30mA RCD. The cable goes directly from the dis board up the wall in trunking to the roof space where it is clipped to the joists before coming down the opposite wall under plastic capping which has been drylined over, feeds two double sockets and one single, then goes back up the wall into the loft before it comes down the adjacent wall in two drops for two double sockets and finally back up the wall into the centre of the ceiling for a garage door motor.

I did the first fix about 6 months ago and the second fix has just been done.

The live to earth IR is not brilliant at about 120 M Ohm but obviously OK, the problem is when I screw any of the sockets into the back boxes the IR goes down to 2 M Ohm. The boxes are just screwed to thermalite blocks and they are not earthed. I have tried different sockets but no difference. If I push the sockets into the boxes but don't screw them in it's OK.

I have carried out end to end tests and all OK, As far as I can I have inspected the cables and cannot see any damage.

It doesn't make sense to me; any thoughts.

Cheers
 
When you say "when I screw any of the sockets into the back boxes the IR goes down to 2 M Ohm" have you really tried one at a time?

You say you have tried other sockets, so that would appear to rule that out as a problem, assuming they are not all from the same batch of course.

2 Meg is odd, not a short but very low for any usable insulation and not something to be content with (as you are very ware). I guess the CPC is good (as you seem to be properly testing) but can you try putting a connection between E and the back boxes to see if it is the connection from being screwed in, or (if not) the physical pressure that is a factor.
 
When you say "live to earth IR" can I just check you actually mean "line and neutral tied together, to earth" and you're not just testing line to earth (with the N still in the N bar)?

Because if the latter, then you're measuring the resistance between the wall and your actual earth, which might well be 2MΩ, and isn't a fault.

If the former, then I'll have to ponder some more.
 
If not USB and are metal back boxes .. This makes sense.

Poor 120M is raising damp patch in thermalite live ?
(some damage / damp un earthed connection)..clipped ?
Measure L-> screws in termalite wall .... Thermalite has floated to L not earth !!
.... or am I taking deductive reasoning too far ..
 
USB sockets should be irrelevant as they have isolating transformers like shaver sockets.
 
.... or am I taking deductive reasoning too far ..
Perhaps, the only other way of thinking is the new circuit has a fault to earth, but the CPC isn't continuous for the entire circuit, perhaps a damaged cable. When the sockets connect to the wall boxes that are earthed through the damp wall the true circuit insulation resistance is shown. But I assume r1+r2 was already carried out and a pass?
 
I had a fault like this in the past. Here is what I worked out was going on:

DSC_1105.JPG

There was an old aerial cable buried in the paster near one of the sockets I was testing. When the socket was screwed into the back box, I measured 0.3MΩ (L+N) to E at the socket (and at all other sockets); when socket was disconnected >999MΩ; measured at the DB, 1.6kΩ (N to E) due to the actual fault. There was only one fault - the 0.3MΩ was just the resistance between the back box and the connection to E (probably via the aerial earth).
 
The most likely scenario does seem to be that the line conductor is faulted to the blockwork e.g. by a nail, but the blockwork is not in contact with the CPC e.g. via real earth.

Suppose the the fault gives 2MΩ from line to blockwork but the wall is standing on a good dryish membrane or damp proof course giving 120MΩ between the blockwork and real earth. You'll read the 120MΩ to the CPC when it's in the earth bar of the CU, if that's earthed to real earth and not in good contact with the block. But when a socket is screwed home and the CPC is connected to the back box, the path is now from line through the fault and back to the CPC not through the membrane, so it reads 2MΩ.
 
Unearthed metal back box's, when you screw in the sockets they try to earth through the blockwork?
If the main CPC is OK I would expect it to go to low-R if it were simply the box coming in contact, but to be checked.
After all it is either related to the box being earthed, or (more likely?) they physical force of being crewed in doing something to the cable.
 
or (more likely?) they physical force of being screwed in doing something to the cable.

However, the OP says when any of the sockets are screwed in, the same thing happens, so I'd infer that the change in IR is caused by connecting the CPC via the box to the mass of the wall.
 
However, the OP says when any of the sockets are screwed in, the same thing happens, so I'd infer that the change in IR is caused by connecting the CPC via the box to the mass of the wall.
Good point, but usually you would be testing to the CPC (already connected to earth)? I.e. box to socket is already earthed.
 
Not if the wall is standing on a membrane that provides higher insulation that the blockwork of the wall itself.

My troubleshooting method would be first to disconnect all conductors at the CU and prove that I get the 2MΩ between line and at least one box. Then, split the line at each point and test to the box to find the faulty section.
 
Thanks for all of your replies. I will go back there this week to further investigate but I am thinking the most likely cause is a nail through the cable.

Just to clarify a few points raised; the low IR is between line and CPC with nothing connected in the CU. Some of the sockets are metal faceplate and some are plastic. I have tried screwing each in individually and I get the same result and it is as soon as the screw is screwed into the backbox so nothing to do with pressure on the cables. R1R2 is 0.34 Ohms. Using 500v for the testing. The wall is quite new so is probably still damp.
Cheers
 

Reply to Low IR on new radial circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
592
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
546
Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
929
Hello, Last year I had some electrical work completed in my house (New CU, SWA for garage, downlights) I informed the electrician that I will be...
Replies
8
Views
2K
I’m planning a 240V welder circuit in a detached garage with a 100A sub panel. For the 160A or 180A output welders I’m looking at, the conductor...
Replies
5
Views
894

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock