Hi All, I am having problems finding a fault and would appreciate any ideas, I have got an RCD on a ring main and on some sockets all tests are great but on some sockets the RCD is tripping at greater than 40 ms on 5x test any ideas?
On 'Pattesters' website they advise-
When testing modern IT equipment it is not normal to performed a leakage or touch current test; these tests are usually used on older equipment in place of the 500 Volt insulation test.
However in my copy of the IEE they say that touch current test should...
hello all, im a jib graded electrician just finished my 2392 course and have my 2391 course booked for the end of september. im pretty as green as grass as testing goes as i have not a great deal of experence. ive be asked to test a number of circuits and the sockets all have metal back boxes...
Hi guys,
Just wondering what qualifications enable me to test emergency lighting systems?. I have level 2 and level 3 City and Guilds 2330 and my 17th edition.
My Client asked if i could do it for him tomorrow. I have done a bit of reading on the subject, regulations etc. but cant find that...
Hi folks, client has requested PIR on a property with disconnected supply (not sure how disconnection has been effected). Property has been empty for a long time and potential buyer (retired electrician - no pressure) wants to know as much as possible to see if price can be negotiated down...
SW1970
Thread
disconnected
disconnection
earth
pir
property
supply
testing
tests
How can I work out the P-N figure of eight readings and the R1and R2 readings from the end to end readings of the ring cct.
This is because our certs are typed up as we go along on site, and I only do the end to end tests on the ring.
Can anyone help pls.
Hi all, what will be the frequency of testing for fixed equipment as stated in cop? It has stationery but not fixed items ie hand dryers?Also what exactly do they mean by initial frequency. Is this the first test after purchase.If so when is the next insp required??Last thing my supernova...
Hi all During r1 r2, ELI and PFC tests of a lighting circuit would it be a problem to leave lamps and ballasts etc in GN3 shows them out but I can't see a problem
Hello, can some give me some advice on what the problem could be with the ring final im checking before changing the cu, did at test with line & netural joined and tested to earth at 250v and got 25Mohms so went to test at 500v and got 0.35Mohm.
thanks jimmy
Hey peeps, looking at the new 1730 MFT from Megger, currently using the 1553.
Just wanted to know if any of you are using it and what you think?
Also interested in the no trip test speed, is it much faster??? How long do the batteries last...etc.
Any info would be much appreciated.
Came across an advert on the job center online for a PAT engineer in the Birmingham area with an average 300 tests a day able to be carried out.
Dont know if it allows me to post the link but:-
Directgov jobs and skills search - Job details
Some average numbers there, discuss??
russty
Thread
courses
degrees
engineer
engineering
pat
pat testing
salary
students
tests
What is the proper procedure for ELI testing circuits with UPS back up, ie radial circuits under computor room floors?
Do you test with the mains bypass connected? with the UPS/ mains in normal operation? or in UPS status only?, ie mains failure.
Thanks.