Hi just inherited a second fix job, it has a heatrae sadia amptec electric bolier fitted rated at 10-12kw ready for wiring there has been a 10mm t&e cable installed to a double recessed box by the boiler. It also has an electric shower fitted so i need to install the RL1 relay from heatrae sadia so they both dont come on together, the mcb in the consumer unit is 50amp the questions i have are as follows -

1 - do i need 10mm heat resitant flex in to the boiler?
2 - who makes 50amp 2gang double pole switches?
3 - should i use a small con unit on the 10mm to split thing up
4 - can i take the feed for the programmer and control of the boiler feed obviously fused down or take the controls feed from an adjacent socket which would mean two seperate supplies on to boiler
any help if you have installed one apprieciated.
 
1. I would just install within mechanical protection if this is not possible heat res

2.mk

3. If there are spare ways in the cu why separate them all within the same feed to the house anyway

4. I would fuse the main feed down within an adaptable box as it would be better on the same feed for peace of mind if not possible make sure it's labeled at both sides of the installation and wrote on the test sheet
 
MK Logic 50A 2G DP SWITCH
www.directtradesupplies.co.uk/mk-logic-...
MK Logic K5205 WHI Supplied with 8 self-adhesive plastic identification labels marked hob, fan, oven, ....
 
If it's 12kw then make sure that 10mm is adequate. I have usually found that 12kw units are on 16mm with a 63a mcb.
 
cheers there are no spare ways and the route back to the main cu is origional floor with over boarded with oak boards so customer doesnt want them disturbed, will come out from the dp switch and the split for control wiring just didnt know if this would be too near the 50a load as i cant allow for diversity on water heating
 
FS cables are the best for buying specialist cables from. Cut any length overnight delivery.
I have wired a few over the past couple of years and have always used silocone cable. Heat resistant and will carry the load.
 
It's really a case of following manufacturers instructions here if it's not obvious. If the cable enters a cool part of the boiler and terminates away from any heat source, then it's unlikely that it will need to be heat-res.
 