Hi, does anybody on here have any recommendations for a relay that will switch (energise) @ 100mA 24 Volts, only need 1 x N/O contact for this
Thanks
 
I don't really understand what you're looking for, are you after a current sensing relay? Maybe you can give more details about the application...
 
I am looking for recommendations for a relay with a coil that will energise from a 24 Volt DC 100 mA pnp signal, I then wish to pass a 24 volt 500 mA 24 volt dc through the n/o contacts, cheers
 
There's many options depending on form factor, mounting type, enclosure specs etc.
We've used the Omron G5CA in the past. RS components sell them they're cheap and available in high sensitivity as well. Try here.
 
We only use PCB mount but you could have a look at these if you need DIN mount, apparently they can be transistor driven. I see there's a big price difference though so it might be worth using the checking out the alternatives.
 
Positive /negitive/positive transistor switching.....You can used "handy relays" available in all alarm suppliers. I presume this is a fire alarm out put signal as in gents 100mA outputs
 
Looks good but I think the one I sourced via RS will do the job plus its DIN rail mountable, this isn't a fire alarm application, it is to be used for machine control, thanks for all the input and advice, cheers
 