Can the socket wait until your dad is back?
I’m just concerned you won’t have the quals to sign off the test certificate.
 
I don't like the idea. The present user might have a specific purpose in mind for the socket, but as it is in a general purpose area (rather than say within an equipment enclosure) other people might use it for anything. A 10A MCB or RCBO won't trip at 13A, it will be in the grey area between In (the rated current) and 1.45xIn (the current at which it must trip.) So no-one will necessarily realise anything is wrong, but the device could routinely be run above In. It falls foul of the requirement Iz>=In<=Ib and is therefore bad design.

OTOH it is more likely to nuisance-trip on inrush too, e.g. a microwave that takes 5A can trip a B10 when you press the start button. Nuisance trips are bad not only because they are a nuisance, but because they make people complacent about resetting circuit breakers. 'Oh, that one always trips, don't worry about it' and don't then associate a trip with an electrical fault.

These are problems that you can foresee and avoid, so IMO you should avoid them. Not having the right device in the van is not justification for poor design.
 

Reply to 10A RCBO For a radial with 1 socket in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
904
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
584
Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
889
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
580
Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
706

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock