Customer has a 12v extractor fan (broken) that has a permanent 12v supply to it with the lights switched on or off. Apparently it used to only come on when the light was switched on.

Apparently nobody has changed anything since it worked with the light.

Not sure how this is possible?

Any ideas....
 
Probably has an integral timer/run on and would need a permenant supply...and the overun timer wasn't set to run on!
 
poss humidity sensor inside? so has perm supply for humidity, switched supply, and neutral.. all 12v via transformer.
note normally humidity sensor is in transformer.
 
No fan is just a basic 12v live in neutral out. No timer etc.

However next to isolator is what looks like the transformer. Haven't opened it up yet.

Just suprised that it now has a permant feed whether lights are on or of, yet at some point it never. Strange....
 
fan is controlled by the transformer which would also be the timer take 3 core to transformer and 2 core to fan prob fault with the timer
 
What's the timer got to do with the operation of the lights though. There's a permant feed, not operated by light switch!
 
would be a permanent live and switched live to the timer fan controlled from there open up timer/transformer and have a test bet its putting out 12v permanently
 
Apparently it used to only come on when the light was switched on.

Apparently nobody has changed anything since it worked with the light.

Not sure how this is possible?

Any ideas....



Always listen to what the customer has to say,,,BUT NEVER believe what they say unless YOU can prove it.
 