Garage radial running from 32 Amp MCB with 4mm T/E supplying Multiple 13 amp sockets which are only used one at a time .


New compressor 2200 watts during normal operation but increases to 6600 on start up . . Can a 13 Amp socket safely handle the initial motor start up phase or do I need a 32 Amp socket for compressor
 
It's not the socket that matters but the fuse in the plug, and whether the starting current will blow a 13A fuse depends on both current and time. 6600VA requires 28A at 230V, which a 13A fuse will take for a couple of seconds at the very least, possibly a minute or more. Most small compressors start in less than a second so it should be fine, although the fuse might fatigue and fail after a period of time.

Alternatively, a 16A socket with suitable MCB would be perfectly OK. There's no need to go up to 32A.
 
It's not the socket that matters but the fuse in the plug, and whether the starting current will blow a 13A fuse depends on both current and time. 6600VA requires 28A at 230V, which a 13A fuse will take for a couple of seconds at the very least, possibly a minute or more. Most small compressors start in less than a second so it should be fine, although the fuse might fatigue and fail after a period of time.

Alternatively, a 16A socket with suitable MCB would be perfectly OK. There's no need to go up to 32A.
So would the best option be to do away with the plug and get it hard wired into an isolation switch
 
TBH I would probably look at using a 16 amp socket as Lucien has alluded to, guaranteed the compressor will kick in just as you start to use something else and it all goes off.

Depending on your circuit arrangement this should be fairly easy to sort out without too much expense.
 
Why not try it with a 13A plug and see how it goes? The rating and fuse mean it is safe from overload, but as Lucian points out you might fatigue the fuse after some time. If it proves troublesome then look at a 16A commando socket and a 16A C-curve MCB just for that.

If there is any risk from the supply MCB tripping and a loss of lights (e.g. workshop with dangerous tools in the dark) you might consdier fitting emergancy lighting so on power fail for any reason you are not in total darkness.
 
Advice please


Garage radial running from 32 Amp MCB with 4mm T/E supplying Multiple 13 amp sockets which are only used one at a time .


New compressor 2200 watts during normal operation but increases to 6600 on start up . . Can a 13 Amp socket safely handle the initial motor start up phase or do I need a 32 Amp socket for compressor
It's a recommendation only that loads of 2 kw and above should be on a dedicated circuit.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
london
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
13 Amp socket
Prefix
N/A
Forum
Electrical Engineering Chat
Start date
Last reply date
Replies
6

Thread Tags

Advert

Thread statistics

Created
ukmicky,
Last reply from
Pete999,
Replies
6
Views
2,490

Advert

Back
Top