If it were something that I had to do, I would have the RFC on 32A as normal and a separate isolation switch and 16A MCB 'FCU' just for the 16A socket.
As with the long thread on two rings on one MCB a couple of months ago, it is difficult to point to a 16A breaker-fed load on an RFC as being much of a danger compared to 20A from a double 13A-fed sockets.
But to me the main problem is when something very odd like this is done, the next person to fiddle with the system has a much higher risk of causing danger due to it not being correctly documents and/or the documentation not being read by said person.
One benefit of the RFC comes from the diversity possible from multiple loads below 13A along with a 30A fuse / 32A MCB supply OCPD. Reducing that to allow for a very unusual socket for domestic work seems wrong. Equally not having a 16A socket limited to 16-20A MCB is also a hazard, as even with a fixed load one might assume a higher chance of flex damage if it can be plugged in and out.
[automerge]1600372347[/automerge]
Also I don't not think you can ever safely assume that a load plugged in to a socket is fixed. What you originally fitted it for might be, but next occupant might well decide to plug in a totally different appliance / extension cable to the socket. So the socket must be overload protected.
As with the long thread on two rings on one MCB a couple of months ago, it is difficult to point to a 16A breaker-fed load on an RFC as being much of a danger compared to 20A from a double 13A-fed sockets.
But to me the main problem is when something very odd like this is done, the next person to fiddle with the system has a much higher risk of causing danger due to it not being correctly documents and/or the documentation not being read by said person.
One benefit of the RFC comes from the diversity possible from multiple loads below 13A along with a 30A fuse / 32A MCB supply OCPD. Reducing that to allow for a very unusual socket for domestic work seems wrong. Equally not having a 16A socket limited to 16-20A MCB is also a hazard, as even with a fixed load one might assume a higher chance of flex damage if it can be plugged in and out.
[automerge]1600372347[/automerge]
Also I don't not think you can ever safely assume that a load plugged in to a socket is fixed. What you originally fitted it for might be, but next occupant might well decide to plug in a totally different appliance / extension cable to the socket. So the socket must be overload protected.