I suggest you read the thread. Then tell me where I have complained. And I suggest @Taylortwocities keep his suggestions to himself.
All say a 16A appliance cannot be taken off a 32A ring because the regs say so, even though it can be done quite safely - and I have seen this done. Fine, I go with that, as we are all best going one way
I pointed out splitting the ring into two 16A radials, bringing up the point that a radial created out of the split may have 13A sockets on it, but a 16A commercial socket/plug can be fitted for a 16A appliance - unlike the Continent we do not have 16A sockets/plugs. I see no one took this one up.
Mainly because it's clearly described in the regulations
A ring, and multi-radials are designed around the use of bs1363 fittings, they each are protected by a fuse up to 13A - or have one in the appropriate plug.
Industrial 16A and so on type fittings do not have any guarantee of a fuse protecting the cables, flexes, or end appliance.
Therefore they need to realistically be on single dedicated radials, generally you use these where greater than 13A is required and therefore you are unlikely to be able to apply diversity sufficient to manage multiple 16A outlets.
I do suggest that you familiarise yourself with the regulations rather than just decide what should be ok even if its not allowed by them.