I wouldn't be changing those except removal of MCB's and replacing them with RCBO's ........... on the circuits that need RCD protection
There is already an up front RCD protecting the left hand consumer unit. The photo's aren't clear enough to show its rating however.
 
Effectively there is RCD protection to the consumer units and if it is 30mA then adding the additional sockets would not be a problem, 100mA would not be acceptable for a circuit modification.
However the single RCD is not a good arrangement as it does not allow circuit level separation on earth faults.
 