I taped each leg up, it's as was wired before. If i'd have mixed the rings up surely the other RCD would spot the imbalance on the other side and that too would trip?
The sockets stay on till there's load getting pulled, ie the fridge is swithched on or kettle or owt else, they run a few seconds and trip. As for the upstairs lights, it just doesn't go on full stop. Yet without the RCD no issues.
Well, ....There's a clue for you , Surely??
) i did like spark68. Long time ago.