Update:- Have been today and did some testing.
No borrowed neutrals exist.
Tried all lighting on same neutral side upstairs lights still weren't happy fed via the RCD, cct tripped straight away as before. Still works with MCB with no RCD protection.
Tested Kitchen ring, wirings sound good IR results and went round with martindales, all skts wired correctly. Transferred ring onto RCD protected side, powered up and plugged and tested each appliance one at a time. Had no problems. (It was very cold last week during board change), possibly had lower IR back then with damp, or there may still be an issue when i come to place 2nd RCD back into board and have rings on seperate RCD's (imbalance issue?) as ideally i want upstairs lighting with downstairs kitchen ring and downstairs lighting with upstairs + (rest of house) ring.
Downstairs lights wiring sound.
Upstairs lights, very low reading between E-N (short), L-E not so clever either of just 28Mohms. Wonder if i have a dodgy JB/light fitting somewhere. Have investigated on suite upstairs inc shaver socket, light fitting connections weren't great but wasn't that. Left in connector block as they need a new light fitting.
Had to leave job earlier than would have liked, back there tomorrow. Normally i'd split the cct in half but as i don't know how it's been wired i'm just checking existing points of interest that i never ammended. Have yet to check spotlights in toilet, loft light and outside lights so there will hopefully be something within them. If not it's a mistake i've made somewhere in fitting the new lights upstairs. Failing that.......which i'm dreading is that all lights are wired soundly and fault exists somewhere i can't get at ie within walls or under floors. Eeeek what's the score if thats the case then? Rewire? I'd love to but thats the last thing the homeowners would want. Surely if tested this would be an instant fail? If left on normal MCB way unprotected by an RCD working but with a fault somewhere? Potentially dangerous and something i'd not like left.
Oh and the smoke detector cct has a very low reading between L-N. Hopefully thats just a dodgy smoke head, otherwise i'll just advise them getting battery fitted one's. Not good but only option if wirings dodgy.
Never again am i not going to test existing wiring before even changing a single socket or switch!!!
I've learnt my lesson........ the hard way!
Anymore advice forthcoming would be much appreciated cheers.