Jonathan Swift

There are two questions that Ive been unable to locate in the regs book;

1. If the line conductor is 10mm2, the min size of of an associated Surge Protection Device connection conductor is?

2. A 230 V 30 A radial circuit is protected by a BS 3036 device. If the value of earth loop impedance for the circuit is 2.3@ (I think means amps?), disconnection under line/earth fault condtion will occur in:

2s, 4s, 5s, 3s?

Thanks
 
Not sure on 1 as i'm not at my book.

For 2 you need to use the supplied values to work out the prospective fault current and use the tables in appx 3 to find the answer.
 
  • Like
Reactions: Jonathan Swift
As for the second question it will be ohms and ohms law

You will need to find the time curve chart for the actual tabulated trio times for 3036 fuses
 
Not sure on 1 as i'm not at my book.

For 2 you need to use the supplied values to work out the prospective fault current and use the tables in appx 3 to find the answer.
Many thanks, so @ was in fact Ohms and not Amps. 230/2.3 = 100. In tables is 3 seconds. Cheers
 
  • Like
Reactions: Andy78
I have done, on page 170. But it doesnt correspond to the apparent correct answer on the exam paper...
 
the exam paper states 4mm, 6mm, 10mm or 2.5mm. With the correct answer apparently being 4mm
 
I feel a John Ward moment coming on and wanting to pass 100a through a 3Oa fuse wire to see how long it takes to blow...

I bet it’s a dang sight longer than a few seconds :)
 
Many thanks, so @ was in fact Ohms and not Amps. 230/2.3 = 100. In tables is 3 seconds. Cheers
I'll take your word for that as not with my book to see the tables ... but sounds good.
Annoying misprint, but maybe it is to do with a technical error with software not recognised the ohm symbol. What study material are you using ?
 
  • Like
Reactions: DPG
Ive used quite a few but these two are from sparky facts online page. Thanks for your help, I'm wondering if the second question is just the wrong answer
 
the exam paper states 4mm, 6mm, 10mm or 2.5mm. With the correct answer apparently being 4mm
Hi - yes, I thought that might happen. The reg clearly states the connection to MET is a minimum of 6mm and 2.5mm min for the live. The live size used depends on the circuit overload protective device, which you are not given. If it was 32A, I’d pick 6mm etc. With the Wylex board mounted SPD they provide 16mm (edit - maybe 10mm, brain fade sorry) for all connections.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
18 th Edition questions
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
12

Advert

Thread statistics

Created
Jonathan Swift,
Last reply from
Wilko,
Replies
12
Views
2,174

Advert