any ideas would be gratefully accepted.

went to a job today. no upstairs lighting at all, did various tests, 240v at the CU, 195v at several of the fittings.

lighting is loop in ceiling roses/fittings, switches are line in and swl, mixture of dimmers and switches.

to bathroom fans on isolators, pullcords in bathrooms to operate lights (and assume switch fans - I couldn't test, not enough voltage)

circuit is small in length and number of fittings.

has anyone come across this before ?
 
first of all, have you tested L-E at fittings? if that gives you 240V, then it's a neutral fault.
 
240V at the output of the fuse I assume? L-N? L-E? N-E?
195V across what? Loop at the rose? L-N? L-E? N-E?
L-E and L-N loop impedance at the fittings?
 
242v at output of fuse in CU L-N
195V at fittings L-N
even the first fitting does not work
there is a two-way switch in the downstairs, no neutrals, just line conductors - this doesn't work for the landing light either

it must be a bad neutral somewhere, the cable is in really good shape, no signs of any degradation (what I can see anyway)

thanks to all
 
went to a job today. no upstairs lighting at all, did various tests, 240v at the CU, 195v at several of the fittings.

When you say "no upstairs lighting at all", do you mean that there was not enough current to light a lamp? If you are measuring this "195V" with no load on the circuit, then there's probably a break in the supply and the voltage you are measuring is a phantom or induced voltage.

What is the voltage with, say, an ordinary GLS lamp across the supply? If zero, or close, then it's a break rather than a resistive fault.
 
242v at output of fuse in CU L-N
195V at fittings L-N
even the first fitting does not work
there is a two-way switch in the downstairs, no neutrals, just line conductors - this doesn't work for the landing light either

it must be a bad neutral somewhere, the cable is in really good shape, no signs of any degradation (what I can see anyway)

thanks to all

Well, that will tell you where to start looking for the fault on this circuit then, won't it! ...lol!!
 
242v at output of fuse in CU L-N
195V at fittings L-N
even the first fitting does not work
there is a two-way switch in the downstairs, no neutrals, just line conductors - this doesn't work for the landing light either

it must be a bad neutral somewhere, the cable is in really good shape, no signs of any degradation (what I can see anyway)

thanks to all

Did you test for voltage between L-E and if you did what voltage was present?
 
Whats going on?!? Going to a fault with 50 volts lost and not testing between all conductors and then no IR or continuity tests?

Were you not taught this in your apprenticeship? Fault finding and rectification, spent about half my 3rd year doing it and still struggle with faults in the first few years after that.

Sounds like a break on the feed from the CU and first pendant, I try a long lead method on each conductor back to the CU and see if results are consistent between L-N and slightly higher on E if its wired in twin. If not its hammer out time!
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
195v on a domestic lighting circuit
Prefix
N/A
Forum
Domestic Electrician Forum
Start date
Last reply date
Replies
14
Unsolved
--

Advert

Thread statistics

Created
ianbrookes,
Last reply from
Adam W,
Replies
14
Views
3,465

Advert

Back
Top