If I understand you correctly, the supply is taken from two of the three line conductors of a 3-phase supply, without a connection to neutral. This makes it a single-phase machine, not two-phase. It just happens to be 400V, therefore the necessary voltage is found between two line conductors, rather than line and neutral. The idea is that by working at 400V where this is available, the current rating is reduced without the complexity and cost of a three-phase machine. Others have mentioned welders, indeed my own portable single-phase welder is switchable between 230 and 400V. At the workshop, I have many 16A 3-phase supplies and it will run on one of those on its 400V setting. However when set to 230V it requires a 32A single-phase circuit.
Two-phase systems were used in the past, they have two phases and a neutral or even two phases and two neutrals, and give a rotating field in a motor much like a 3-phase supply but with different phase angles. Two phases out of a 3-phase supply are not the same thing.
Lucien