I have to put in a 20A supply for a cabinet in a Spar shop.

I have used the voltage drop calculator and it has come out at 2.5mm t & e. It's only a 18m run ................ Some people use 4mm t & e out of habit for such an installation. Why? The old belt and braces routine!

Anyone got any opinions?
 
then if your VD calc. is OK, then 2.5mm will do. i've done a few 16A points for spar fridge cabinets, and always use 2.5mm if clipped direct.
 